Modes Of Building
Abdul Malik Memon
Asalam-o-alaikum,
                              what the term mode means and how we compute the mode?
I've been told that mode is used to determine the time period of the building and the mode 1 has the maximum time period so no need to check further mode. is that correct?
and how we determine the mass participation of building through mode?
thanks.
Modes are deformed shapes. A building may have a primary mode a number of other modes. You can easily check the modes and associated time period by completing a modal analysis and going through the results. For cases where there is a forcing function producing harmonics (like pump, compressor foundations) mass participation becomes meaning less and every mode is important. Under such case we want to design a structure so that none of the modes fall within the frequency of forcing function. If that is unavoidable, we check response of structure under resonance and make sure the amplitudes under resonance are below allowable. For seismic application, mass participation is important. Generally, people ignore modes having less than 5% mass participation for seismic.
In addition to that, following excerpt (attached pdf) from my dissertation might be useful.
Also it is not necessary that mode 1 in ETABS is always the fundamental mode.
In ETABS mode 1 will have the highest time period and so on....but also look at how much mass of the building is actually active in that mode.
Building modes should be well separated; translational from torsional. What that means is T of X,Y modes should have difference from RZ mode. For example 2 seconds and 6 seconds is good difference, but 2 seconds and 2.5 seconds is of concern.
Look at the comparative values of mass participation in X,Y and in RZ.
For example if X has 45% mass participation, Y has 55% and RZ has 60% mass participation. These are let's say mode 1, mode 2 and mode 3 respectively.
As you can see, the relative mass contribution in translational (max of X & Y is 55%) and torsional mode (60%) are quite close. This should not be a problem if Mode 1&2 and Mode 3 are well separated.
Now you can look at this problem in another way (by looking at a particular mode only).
For example in above example Mode was in X with 45% mass vibrating in X direction and let's say 5% in Y and remaining 50% in torsion RZ.
Now it's quite difficult to determine in such case, that this is a torsional mode or a translational mode because 45% and 50% are very near.
But if it was 75% in X and remaining in RZ, that would be a clear translational mode.
You should include enough number of modes in ETABS so that there is atleast 90% of the building mass being involved in vibration. Otherwise increase number of modes. A rule of thumb would be No. of storeys / 10.
A rigid diaphragms will have 3 degrees of freedom so 3 modes. Modes are degrees of freedom of a building. DOFs are the number of ways a building is free to vibrate. So a 5 storey structure with rigid diaphragms will have 15 active DOFs and so 15 modes, but some modes are less active and some more.
Use Eigenvalue analysis, if the building is regular, stiffness and mass distribution is regular. Otherwise use RITZ which will capture the most effective modes first.
A good explanation by Ashraf HabibUllah is given here for these two types of mode analysis.
I hope Mr. Badr Muneeb can shed some more light on this, as this video was in AIT where he was present too.
There are also other posts in this forum relating to mode shapes. For example
Ritz Analysis Problem
and
Etabs 2013 - Story Shear, Deflections And Time Period
I hope all this background will help you to understand modes shapes of building. Cheers!
excerpt.pdf
  • 4 weeks later...
18 hours ago, Engr Fayaz Ahmad said:
one of our teacher told us not run the modal analysis while  analyzing a structure in sap or etabs   i don't understand why?
That makes no sense. You should consider it.
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik