SAP DESIGN
Nouman Mukhtar
I have a beam of 6.6m length. 3 point loads of 35kN are acting at 1.65m c/c. Section modulus required is 615,790mm3, It means if we use Beam size of 500x4x150x8 (Section modulus = 761,697), it must pass with stress ratio of 0.808 (615,790 / 761,697). But designing in SAP for same beam and loading is giving me stress ratio of 4.041. Why there is huge difference?
Model is attached herewith.
please guide me as it is little urgent.
Beam 1.SDB
Beam 1.SDB
SAP2000 is calculating the moment resistance of beam considering all design limit states like lateral torsional buckling, maximum unrestrained length etc. What you are referencing is Mr= Mf/Sx which is not the only governing parameter. Strength of beam depends upon its unbraced length.
SAP2K Output.pdf
Strength would't effect much as I explained above. Also your member web is Class 4 or Slender Sections (I believe thats what they call them in US). I would never do a non-compact section design on a software. Use software for analysis only and design it manually.
Umer bhai if you have any manual or spread sheet for simply supported beams, continuous beams, frames design please share it.
Normally we use non compact sections and even slender sections for design and allowable stresses are adjusted accordingly. The main purpose is to control the weight of building and so we also use slender sections.
Please guide what can be consequences of using non compact and slender sections.
I have only done one Class 4/ Slender section (it was an angle) design. My line of work has more standard sections. Class 4/ Slender Sections fail locally before yield moment can be obtained thus greatly reducing section capacity. If your line of work has a lot of Slender Sections, I would advise you to get a book and use the examples in the book to understand the design of these sections. These sections are common in pre-engineered building industry and if you deal with them on daily basis, get a reference book. That would help you.
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik