foundation and slab suggestion
Sohaib Iqbal
please give me suggestions for the designing of this project. ie pile foundation and type of slab. bearing capacity is too low 1.04 tsf. we are discusing abt providing pile fondation and for slab , post tensioning or waffle slab. is it safe for 44ft by 46ft span?
i have uploaded the plan.  G+5 stories.
ground floor plan.pdf
Sohaib,
You can do a RAFT foundation supported on piles that can support your building columns. In order to design the piles you need to ask geotechnical consultant to provide you with skin friction values that can be used to do the geotechnical design of pile. Once that is done, you need to  do structural design of pile. Pile design is fairly simple. You can do driven steel or concrete piles based on geotech recommendation.
For the slab, 44' by 66' is not a big span. You can design it using Safe. You provide beams to reduce the slab thickness.
Thanks Umer bhai. we want flat slab so we are going for post tensioning in order to reduce thickness of slab. can we use ribbed slab or waffle? some one told me to to design normal slab like a hollow slab if thickness is act 14 inch or 16 inch. can we do this?
That is not correct.
Your span is not big. You can do a simple waffle or one way. For one way slab just add more beams and divide your length into smaller panels.
You can also do a post-tensioned flat slab as long as you can design it and there is an experienced contractor who can execute the job.
Dear Mr Iqbal
Correct me if I am wrong.
Suggestions
G+5 is not too much load we are not talking about. And bearing capacity is reasonably fine considering the magnitude of building. You can easily do the foundation with mat type. Its 44' span that must be govern as it will become one way;. In the you will get too much top moment. Moreover as most of load is concentrated on the edges it is recommended to cantilver your foundation as much as you can,
Slabs
For slab just go for one way slab with main beams are 44' in length. Please make sure that one way spans shall be around 10 to 14ft. as this will drastic reduces your deflections. Make sure to remain one way slab, otherwise cross beams will create too much torsional moments.
These are suggestions only,
thanks Ahmed. but we want slab without beams ie flat slab . so we are getting very thick slabs. . so load is concentrating at edges and failing raft on soil pressure at edges also at the centre ( below lift wall). we cannot extend raft because of adjacent plots and road.
Instead of uniform thickness, may be you can provide variable thicknesses?
For example, the raft slab at right and left areas can be reduced. You can provide more thickness in middle area where there are columns and walls.
Similarly you can provide a more thick continuous strip footing all along the parameters under the perimeter columns. Then you can add local thickening directly under the edge/corner columns too.
Tie the edge columns with stiff beams at a level above raft (at gf for example) to connect them together and make the whole thing as one unit.
At the end satisfying bearing pressure for this kind of foundation is very difficult at the perimeter, so at any cost you gotta connect them by stiff strip (preferably straps/beams) foundations.
  • 4 weeks later...
waseem bhai what is the procedure to model this type of foundation in SAFE ie strap beams over raft?
my senior did the similar method in a combine footing ie provided strap beam over combine footing to reduce amount of top steel in combine footing. but i didnt get a way to model and analyze it on safe.
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik