Design of Plinth Beams in ETABS
Kasim
1. We provide beams at plinth level all around the building under the walls. These beams rest directly on ground above lean concrete. Should we also model them in ETabs model???? is this practise correct?
 should we Design it Like normal beams, (More conservative) ?. Or for Reduced moment? (As they are supported along the length)
2. During seismic analysis we specify our Range from Base or Basment of The building to the top or from Ground to the top.?
3. should we include Plinth beams in our latteral force resisting system?
thanks.
Yes you should and the reinforcement in them is generally high so provide what you get from ETABS.
There are a number of threads in this forum on this topic. You can see this one:
If you are providing it, you should. Plinth would give stability to your system.
Edited by Ayesha
15 hours ago, Abdul Malik Memon said:
 one thing i would like to ask, as said by Rana Waseem provide same at top at bottom no matter what the results. One conventional practice is to increase the bottom reinforcement by 20% but why?
Moment redistribution. We used to increase bottom by 20% to account for moment redistribution in case the beam becomes simply supported due to plastic hinges. But with this 20% increase, we used to keep pattern live load factor of zero.
Live load factor zero means, in combination we make live load factor zero.? what if we do not make live load factor zero still do we need to increase reinforcement by 20%?
Can we said that a simply supported beam require more bottom reinforcement as compare to fixed?
He is referring to pattern live load not live load.
By increasing 20% +ve steel, you can justify keeping pattern live load factor as zero.
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik