Pile design
Sohaib Iqbal
Sohaib,
I will try to explain to you the procedures involved in designing a pile.
1) Pile design involves meeting the two limit states: Axial and Lateral (also called serviceability for piles)
Considering ULS design for piles, you need a geotechnical report that contains skin friction values for pile design along with recommended factors for tensions, compression and frost loads. Geotechnical report will also provide you either parameters for lateral design or load deflection graphs.
2) Once you have the geotechnical report, you do initial sizing of the pile based on the load. Geotechnical report recommendations will allow you to size the pile based on geotechnical capacity, which is how much load can be transferred from pile to soil based on pile geometry.
3) Once you have sized the piles based on geotechnical, you will need to do structural checks to make sure pile structural capacity is greater than geotechnical capacity.
4) For literature, you can have a look at attached.
Foundation Analysis and Design - FEMA.pdf
20 hours ago, m waqas said:
is buckling of pile prevent the surrounding soil? my kl/r value come to be 133.
For structural design of pile, you need to consider soil horizontal springs that would provide lateral support to pile. Use LPILE software with data from Geotech values.
  • 6 years later...
On 8/28/2016 at 7:43 AM, UmarMakhzumi said:
Sohaib,
How can we add tensile and compressive capacity of pile in etabs
i am not sure if there is an option in ETABS to do it. I would suggest to export reactions to excel and check the reactions against max tensile and compressive capacity of pile.
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik