Failure of columns and beams in Shear in ETABS
Hussain Abid
Dear all
Wat is the reason of failure of columns and beams in Shear in etabs? When I was using default design combos everything was okay but when I used Strength design combos for gravity and seismic only I.e 1.4D+1.7L and 0.9D+1.0E and then enveloped them then above mentioned condition is faced.i changed the sections of many columns these then became OK by some were fail in Shear still.wat might b reason?
There can be a number of reasons.
To start, your model is not correct. Your loading might not be correct. When you say that your beams or columns are failing, it is very easy to check the capacity of beam or column manually and fix the issue. Have you checked your manual capacities and confirmed if there isn't anything wrong with your models. I don't rely on models as they are mostly garbage in and garbage out. Show us your number that you have done and if you don't know how to do that, spend some time on basics and manual calcs.
Columns failing in shear? Thats very rare. Are you sure your models are correct?
Yes u may b right that model isn't OK coz this situation occurred after I had modelled stairs into the structure. I had already analysed the model before modelling of stairs but there weren't any errors and design was also OK.shud I delete stairs n do modelling in SAFE? Secondly by "capacity" ayesha meant moment capacity of sections? If yes then it isn't big deal to calculate and assign loadings.i will present to u all details just buy little bit
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik