Lateral displacement due to earthquake
Ahmad Shabaneh
Hello, I have a question about maximum permissible lateral displacement of RC buildings due to earthquake
I'm modeling  a nine story residential building using ETABS 2015. The results showed that there is a 6.8 cm lateral displacement (not drift) due to EQx in the top story.
I searched for the limit of lateral displacement of RC buildings, but I didn't find a clear results.
Because there is none except that you have to provide sufficient seismic gap between two buildings. If its one free standing building then no limits except inter story drifts.
So if I have one free standing building and the model results showed that the lateral displacement 15 or 20 cm (Large values) then that is not a problem???
Logically it is a problem when a nine or ten stories building displaced that much, but there is no scientific or engineering judgment on this, and this what I can't understand.
Could you please explain that logic?
Furthermore;
seismic inter-story drift is limited to 2.5% of story height. If story height is 3.5m, the allowable inter-story drift is 87.5mm. If all floors were to be within the drift (so code requirements are satisfied) then a 10 story free standing building would have total roof drift of 87.5mmx10=87.5cm. Thats a lot, yes.
But I do not see any limits in code for the seismic total drift as long as you have satisfied the inter-story drifts.
Ofcourse, more the building overall drift, more will be p-delta effects, (that could be huge for a massive tall building).
In wind design, overall drift is limited due to problem of acceleration at top floors. But in a seismic event, obviously human criteria is not something you should aim for.
In wind design, overall drift is limited due to problem of acceleration at top floors. But in a seismic even, obviously human criteria is not something you should aim for.
Thank you Rana for the explanation.
Furthermore;
I think there is a conversion mistake . 87.5mm x0.1= 8.75 cm.This should be the maximum limit of inter-story drift.
AQ, there is nothing wrong with the conversion. I stated "87.5mmx10=87.5cm" which is 87.5mm for each storey x 10 storeys = 875mm = 87.5cm. This is the total drift of top floor relative to base 0,0.
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik