Design Theories
Abdul Malik Memon
Salam,
I hope you all are doing well. while reading, i came across the different design philosophies working state design (WSD), Ultimate Strength Design (USD) and Limit State Design but couldn't figure the exact difference among them. Can you put some light over these theories.
One more what is the difference between secant and tangent modulus of elasticity and when to use them?
Thank you.
WSalaam..
ASD is design based on actual non-factored loads considering reduced material strength capacties. For example, for 100 kN load on a steel beam with yield of 350 MPa, you will design it using 100 Kn load and a strength of 2/3*350 MPa= 232 MPa. The reduction in material strength would provide safety, calculated as ratio of actual strength/ (reduction factor * actual strength). This ratio is called Factor of Safety (FOS). FOS would vary for foundations, steel or concrete design etc.
ULS is based on factored loads (load factor as per the statistical probability of likely hood of occurance causing failure) with reduced material capacites. The reduction in material capacites is lower than what ASD has. Like for steel design, material reduction factor is 0.9 only which is a mere 10% reduction. ULS is improved and currently the way to go in most building codes worldwide. Some building codes even prohibit using ASD.
The following link contains an excellent reply by @EngrUzair about cost Compairson b/w ASD and LRFD.
WSD is same as ASD.
Secant modulus represents elastic behavior between stress and strain values (as it is a straight line) whereas tangent modulus gives you relationship in any portion of stress strain curve (elastic, plastic etc).
Edited by UmarMakhzumi
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik