Difference between tension controlled and under-reinforced sections
Abdul Malik Memon
Salam,
What is the difference between the under reinforced and tension controlled section? Are they same with the exception of strain values of steel.?
Many Thanks
Edited by UmarMakhzumi
Edited title to make the questions more relevant; added tags.
Great question.
Current ACI design (2002 onwards) is based on strain limit and based on that you end up with tension controlled or compression controlled sections. Tension controlled being the sections where strain is steel is equal or greater than the limit provided by code (0.005 I believe).
Previously (1963 to 2002), the reinforcement design was based on reinforcement ratios. This is where the terminology "under-reinforced", "over reinforced" and "balanced reinforcement" comes from.
The simplest word to put this is that any steel that has strain greater than 0.005 (or whatever the code says) at time of concrete failure is termed as tension controlled. Both under-reinforced and balanced reinforcement sections will meet this criteria.
ACI Code has not specified any stain-range for under reinforced beams. They just say that the beam should fail in tension before failure of compression region. By that definition, the tensile strain in steel must have a value of more than 0.002 before the compression strain in concrete reaches 0.003 for under-reinforced section.
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik