Your question is not clear. If you explain your problem in a bit detail, you may get a more specific reply. However, if the purpose of your question is to know about general procedure of interpreting reinforcements given by SAP2000 software, it is given below.
1. When we design a concrete frame in SAP2000, it gives following different types of reinforcement:
a. In case of columns, required areas of main (or vertical) steel bars and lateral (or ties) reinforcement.
b.In case of beams, results are in the form of reinforcement areas for bottom & top main bars as well as stirrups.
2. Given area of steel for column vertical bars is to be converted to suitable number of bars (using theoretical bar areas, as we do for manual calculations) according to code requirements in such a way that the provided steel area is either equal to or a bit more than the area required by SAP2000. Similarly, reinforcement areas given for bottom & top bars of beam members are converted to suitable number & sizes of bars, such that provided steel area is either equal to or a bit more than the area required by the software.
3. Reinforcement areas provided by SAP2000 for column ties & beam stirrups can be converted to suitable tie & stirrup size and spacing, similar to that explained in the following thread for ETABS case:
HTH
Edited by EngrUzair
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik