Simply supported stairs with large slab thickness
Fatima Khalid
Asalamualaikum
I am designing ground+1 240sq yard residential bungalow.. Stair plan is attached.. If i take flight#3 (marked as f3) as simply supported then thickness comes out to be 11"... so do we provide that much thickness for waist slab??
or should i make flight#3 to rest on landing at elev 6'6" and elev 11'6" and adding point load on flight#2 to reduce slab thickness??
Thankyou
Fatima,
You can use a smaller slab thickness and do a deflection check to make sure stairs deflection it is below the maximum allowable. Service Live Load deflection based on Canadian Code should be less than L/360. I don't remember what ACI said, you can look it up.  It should be similar. Other ways to reduce thickness would be to run a beam at the centre of stairs flight. For a stair run like shown above, such a beam would be hidden.
Let us know how it goes.
Flight#3 is designed as simply supported, it is resting on centre of landing at elev 6'6" and centre of landing at elev 11'6". This has reduced the length (L), so the waist slab thickness is reduced from 11'' to 8''. Personally, I don't know whether it is a correct practice to support a flight on landing rather than beam and consider it as simply supported.
 Thank you.
Fatima,
In order for landings to be considered supported so you can consider a smaller length of stairs.
stair length = 'total length - 2 x landing length' , you need to have both Beams C and D at 6'6" level and again have 2 Beams B and C in this case at 11'6" level. In that way both landings are 2 way supported and the stair flight between them can be considered as one way. You will have to design the landings as two way supported on two edges only.
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik