Shear capacity of Column
Fatima Khalid
Asalamualaikum,
If I know any column section, I can compute its section capacity in terms of yield moment using SAP section analysis or Response 2000 softwares.
But if I want to find whether a column is failing in shear or not, what procedure should I use?
For example, I have a column of 6'' x 18'' with 6 #4 bars and ties of #3@6'' c/c. I have done pushover analysis on software, Now I want to check whether column is safe in shear or not. So I note down the internal shear forces of column from the software at each step of pushover analysis and manually compare them with column shear capacity using ;
Column shear capacity = Shear force resistance due to concrete (2 * lamda* fc'^1/2 * bd)
Is this the correct method? or do I need to consider ties as well in resisting shear? If yes, then Vs=Avfyd/s formula will be used for ties resistance or something else?
Thanks for the help
On 10/5/2017 at 10:29 PM, ILYAS said:
factored shear force is determined from free body diagram obtained by cutting through the column ends,with end moments assumed equal to the nominal moments strengths
Good suggestion but what about effect of axial load?
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik