design Floor Slab in Grade
Eko Juwanto
anyone please advice how to design slab rest on grade? anyone have a referen? i have analyse with SAFE, but i still not confirm with the value of k (subgrade modulus) and the load. that the load assign full on the slab or just partial load at the critical location?
thanks
thanks sir, would you please to tell me how to put the load? i've modeling the slab in SAFE then i assign the area spring, and put the surface load, due to uniform load and i get 0 moment
i think i'm wrong in assign the load, i wonder if someone would explain it how to analyse slab on grade using SAFE, i've read the ACI 360, but still not to understand.
1. First of all, you need to understand how to design the slab on grade (SOG) through hand calculations. Later on, you may develop a spreadsheet or use some patent software to do it using a computer.
2. The references given above provide design methods (pca, WRI, COE etc), dealing with different types of SOG (e.g., unreinforced, reinforced concrete, post-tensioned etc.) subjected to various types of loads (uniform, line, wheel & post loads).
3. Before starting the design, you will need to go through the reference available with you (i.e., ACI 360), and
a. Select the SOG type from the Section 7 onwards, applicable to your case.
b. Study the design requirements from the relevant section
c. Determine the type and intensity of various loads, the slab will be subjected to during service.
d. Solve the relevant design examples, given in the appendices of ACI 360 to understand various design parameters, charts, equations & their application to the design.
e. Using the design prameters applicable to your slab, design the SOG by following the procedure adopted in the reference design example.
HTH
Edited by EngrUzair
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik