Depth of Foundation
Shamim Ahmmed
The foundation should be deep enough that it rests on a competent strata. If you have a geotechnical report, the geotechnical engineer would have made a recommendation about minimum depth in it. If you don't have a geotechnical report, generally it is kept below frost with assumption that the strata underlying the raft is competent.
4 hours ago, Shamim Ahmmed said:
what should be the minimum depth(D) of foundation?
It generally depends upon soil bearing capacity & will be recommended by the geotech engineer in soil investigation report (SIR) of a particular site.
In case of non-availability of SIR, even for some nearby site, IMHO foundation depth should not be less than about 3 ft.
  • 7 months later...
a soil report was investigated when water table at depth of 1m,during construction water table raise up to NGL due to seasonal canal runing excavation of foundation is deeper than water table will cause seepage of water in excavation my question is bearing capacity and shear properties of soil  is same in this condition, we can not provide footing at required depth any recomendation
You should create a new topic instead of posting in a totally irrelevant topic.
To answer your question, go for deep foundations like piles.
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik