HI EVERYONE,
I need to know that how to model a beam in etabs, when slab on both sides of it is at different levels? for reference section of Beam is attached. Second question is, in this case do we need some special detailing if yes then what is it.
THANKS
Generally, offsets for beams and slabs are ignored in ETABS to keep modelling simple and error free. Such cases can be analysed manually. Analysis also depends on reinforcement and detailing for slabs. For example, if you don't provide any negative reinforcement in the bottom (mid-height) slab, you won't be transferring any moment in the beam as the top of slab would crack.
On 3/6/2018 at 3:31 AM, Ayesha said:
You can see this post for reinforcement detailing. Just don't provide the top reinforcement in the bottom slab, rest all everything shown there is applicable.
Thanks ayesha your response is really helpful. one last thing " what is the effect of top reinforcement of bottom slab if i provide that"?
I will reply to that but I want to know what do you think what would happen?
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik