Dear Safeians
I ma working on a 22 Storey Building. we have assume a Raft foundation of 5' for it.
Net bearing capacity after overburden relief is 8kip/ft2. And i am getting 10Kip/ft2 soil pressure under service loads at some locations.
one of my friend said use stress averaging to minimise the values as these soil pressures are nodal results of finite elements.
do somebody have any clue how to do that using safe .. or Excel.
Edited by israr_sari
spelling mistake
As far as high-rise design goes, there is always areas of high concentration in a raft. General practice is to ignore them and focus on more general values and see if they are within the allowable limit or not. There is no guideline for stress average. People do it by using their engineering judgement.
Hello Israr,
As madam Ayesha said there are areas of high stress concentration in raft. Could you specify the location where you are getting 10 Kip/ft2. As specified if this pressure is at corners in small concentrations then you can ignore, however if the area is large then need to apply changes to raft design.
Here is an example to explain what I mean by general values:
If you have a shear wall located on a raft foundation and the only area where you have high stresses is under the shear wall, and the rest of raft has values within the acceptable range, then ignore the high values right under shear wall and focus on more general values or focus on the rest of the foundation.
For your case, @Hafsa Azmat has correctly pointed out that averaging wouldn't work or it would be  very limited. For example you can average 11 and 10 E3 zones (The purple colored stresses) as that is more of a concentrated zone. Not all of the raft. Hope that helps.
Yes, you need to do stress averaging which is not very straight forward. I do not rely on software stress averaging as it will average the stresses based on the given length. Imagine if stress at localized area is too high (peak), even after the stress averaging you will get higher stress and the extent will also be too much. You need to develop your own rational approach for stress averaging, or need to adjust meshing some times.
Have you checked the settlements. What is modulus of sub grade that you have taken. If you computed modulus of subgrade then multiply by FOS then you are using ultimate capacity of soil. For geotechnical design that's not workable. Check settlements if they are in range then ok. These are my view only...
@Ahmed Waqar Settlements is within limit which is about 0.8". And Allowed is 2"
Subgrade of Modulus is 186 kip/ft3 with bearing capacity of 8.01 Kip/ft2.
@Rana well Rana i tried to play with meshing .. no-matter what size i adopted  stresses were over and above the limit (there was very less effect of meshing). only stresses came down when i didn't use any kind of meshing. Which is definitely wrong approach... so finally i concluded that i can not bring down these stresses with str ess averaging so need some other solution.
If the stress is over the allowed limit and is distributed on a large area as shown in your image, then it is not called 'stress concentration' locally. You need to increase the soil capacity.
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik