Hi,
In a high rise building, A stepped column(offset column) is formed like shown in the attachment. The lower column section is reducing it's length by 33% to rise above a particular floor(at 6th floor of the 48 storey building). I would like to know whether any bursting effect will occur at the end block of the lower column due to this transition & any guidance of how much transverse reinforcement is required to resist this bursting. thanks in advance
step column.pdf
Hi,
The attached pdf shows the column reducing from 5.4 m to 1.8 m. Please correct me  if I'm wrong, but what I understood from the pdf is there is reduction in column width by 66% not 33%. Well that is huge and sudden reduction in width.  Please Confirm.
Oh sorry. It should be corrected as "reducing it's length to 33%". Yes it is true than it has a drastic reduction of length. Upper column section is almost 6% reinforced to it's maximum. Actually the below section length is provided more than enough as a requirement of architecture
Well as its sudden reduction in width of the column my advice is to consider this solution. Don't consider the reduction of column and instead if possible provide a beam and floating column thereby the floating column will act as point load on beam and you could design your beam for that load. Also stop that 5.4 m width column at that level and don't consider it for upper levels.