I am struck in a small Issue, I am designing a G+4 building, subjected only to Gravity loads, The typical Floor Height is 3.2 meters and Height below the (up to Bottom Of Foundation) Plinth level is 2 meters. Ground floor has a Water tank hence, at that particular location I cant provide a Plinth/ Grade beam as it will crosses the tank so, I have to design that column for a height of 2+3.2-(depth of foundation-24" (Say))- (depth of Roof beam(15")) =4.21 meter (Effective). In my Etabs model when I am removing that Grade beam I am getting OS#5  Error ( Column load Exceeds Euler's Buckling Force), mean that Column is failing in Buckling. On the other hand when I put a grade beam there it is easily passing. But in practical/ at site, it is impossible to provide the beam.
My query is shall I play with Effective length ratio "K" factor to pass that column without beam as I cant increase the size of Column as it is already 9"X24" column, and If I opt to change "K" factor how to calculate it as by default in Etabs "K" value fixed in "1". I am designing the Building for "Intermediate Brace". Kindly provide guidance in  this regard.
On 2/20/2020 at 1:49 PM, SMAQ said:
Hello Mates,
Can anyone please reply in this regard.
Thanks @ Saifuddin18  for your reply. Sure I will do that, but I am wondering why the column is failing in Etabs and how to overcome this error, because Etabs calculate the column forces using "k=1" on conservative side, so playing with "k" vlaue does solve this issue, but I don't know the exact procedure, I was wondering if I can get an idea of how to do that.
Edited by SMAQ
@SMAQ, yes, you can define your own 'k' factors in the program but for that you have to decide your column end conditions first. Etabs automatically calculate the 'k' values based on rotational stiffness of joint considering all connecting members and I presume it to be efficient. There are only few situations in which etabs make mistake with it. However, if it seems to you that etabs is wrong, you can assume the end conditions and do manual design or take help of some secondary program or excel sheet.
P.S: Effective length factor value 'k' will be different in both the axes of the members.
@SMAQ, Sorry for getting late but I have checked and studied your model, analysis done by etabs seems reasonable to me but the design is somehow not acceptable. Etabs is considering the 'k' value for those columns almost near 3. I suggest you to design those columns in some other program or manually.
P.S: When I change the 'k' value to 1 in etabs, the columns passed with 6T16 bars.
Would like to know what you did for the solution.
You have said in your first post that there is a water tank below plinth level. Figure out if the water tank provides bracing to the column. If yes then adjust the unbraced length ratio of the column accordingly.
You can easily calculate the K factor from the charts given in ACI code depending on whether your column is part of braced or unbraced frame.
@Saifuddin18, please dont be sorry. However what I did is I tried to design it in PROKON with the loads as under
P=1215 kN, Mx ( Bottom) = 9.071 Knm, Mx (Top) = 25.3 kNm, My (Bottom) = 23.06 kNm, My (Top) = 7.3 kNm. I took the partially Fixed end conditions. When I design as per BS code its passing and ACI code it is failing in Buckling.
Now I am thinking to connect it with plinth beam as the pattern in attached pic as I am not getting any Idea, and frankly I don't have idea to calculate the "k" value as per ACI-318.
Also You mentioned the model is showing "k" calue > 3, But the model I see the "k" Value as "1" only. I dont know some thing is wrong.
@SMAQ, I think you took the moments in wrong directions(Mx instead of My and vice versa) in PROKON[considering column at grid K'8].
Further, how much length have you considered in PROKON and you considered columns to be braced or unbraced?
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik