Column Buckilng In Etabs
SMAQ
Hello Mates,
I am struck in a small Issue, I am designing a G+4 building, subjected only to Gravity loads, The typical Floor Height is 3.2 meters and Height below the (up to Bottom Of Foundation) Plinth level is 2 meters. Ground floor has a Water tank hence, at that particular location I cant provide a Plinth/ Grade beam as it will crosses the tank so, I have to design that column for a height of 2+3.2-(depth of foundation-24" (Say))- (depth of Roof beam(15")) =4.21 meter (Effective). In my Etabs model when I am removing that Grade beam I am getting OS#5  Error ( Column load Exceeds Euler's Buckling Force), mean that Column is failing in Buckling. On the other hand when I put a grade beam there it is easily passing. But in practical/ at site, it is impossible to provide the beam.
My query is shall I play with Effective length ratio "K" factor to pass that column without beam as I cant increase the size of Column as it is already 9"X24" column, and If I opt to change "K" factor how to calculate it as by default in Etabs "K" value fixed in "1". I am designing the Building for "Intermediate Brace". Kindly provide guidance in  this regard.
On 2/20/2020 at 1:49 PM, SMAQ said:
Hello Mates,
Can anyone please reply in this regard.
Thanks @ Saifuddin18  for your reply. Sure I will do that, but I am wondering why the column is failing in Etabs and how to overcome this error, because Etabs calculate the column forces using "k=1" on conservative side, so playing with "k" vlaue does solve this issue, but I don't know the exact procedure, I was wondering if I can get an idea of how to do that.
Edited by SMAQ
@SMAQ, yes, you can define your own 'k' factors in the program but for that you have to decide your column end conditions first. Etabs automatically calculate the 'k' values based on rotational stiffness of joint considering all connecting members and I presume it to be efficient. There are only few situations in which etabs make mistake with it. However, if it seems to you that etabs is wrong, you can assume the end conditions and do manual design or take help of some secondary program or excel sheet.
P.S: Effective length factor value 'k' will be different in both the axes of the members.
@SMAQ, Sorry for getting late but I have checked and studied your model, analysis done by etabs seems reasonable to me but the design is somehow not acceptable. Etabs is considering the 'k' value for those columns almost near 3. I suggest you to design those columns in some other program or manually.
P.S: When I change the 'k' value to 1 in etabs, the columns passed with 6T16 bars.
Would like to know what you did for the solution.
You have said in your first post that there is a water tank below plinth level. Figure out if the water tank provides bracing to the column. If yes then adjust the unbraced length ratio of the column accordingly.
You can easily calculate the K factor from the charts given in ACI code depending on whether your column is part of braced or unbraced frame.
@Saifuddin18, please dont be sorry. However what I did is I tried to design it in PROKON with the loads as under
P=1215 kN, Mx ( Bottom) = 9.071 Knm, Mx (Top) = 25.3 kNm, My (Bottom) = 23.06 kNm, My (Top) = 7.3 kNm. I took the partially Fixed end conditions. When I design as per BS code its passing and ACI code it is failing in Buckling.
Now I am thinking to connect it with plinth beam as the pattern in attached pic as I am not getting any Idea, and frankly I don't have idea to calculate the "k" value as per ACI-318.
Also You mentioned the model is showing "k" calue > 3, But the model I see the "k" Value as "1" only. I dont know some thing is wrong.
@SMAQ, I think you took the moments in wrong directions(Mx instead of My and vice versa) in PROKON[considering column at grid K'8].
Further, how much length have you considered in PROKON and you considered columns to be braced or unbraced?
