we usually design stair only for gravity loading because it is designed by using hand calculation that give only gravity resistant detailing. So during earthquake,it may be structural fuse and can't resist lateral load. But,if we draw stair on model,it is shell and can resist lateral load.Not align with reality.
How to solve this problem. In actual condition, Stair can resisit lateral load partially. Plz suggest me how to do and share your experience.
Is it ok if we design stair ramp as crack section analysis?
Edited by Aye Min Khaing
1. Design for gravity initially, then for axial loading (+/-) a part of a braced system.
2. Make slab / landing connection enough to allow for excessive deflection and reversal of loading, with some torsion.
3. Always put staircase inside core walls – i.e. rectangular concrete box - if you can. This allows better detailing and transfer loads via wall.
4. Most stairs in South Asia span between columns (i.e. corner connections), thin slabs with brick on top to make steps; Poor stair / column connection leads to failure in many cases. Also, quality of concrete is often poor.
5. Design stair as diagonal bracing subject to push-pull loads, with the vertical support member / column connection given greater attention; Hence best to have them spanning onto walls between column.... this then leads to "captive column" scenario. Design with full tension laps, with torsional provision in built.
6. Modelling of staircase in computer model will help give idea of behaviour, then you use your engineering judgement to improve the robustness of the staircase slab and its end connections.
7. Remember staircases are used for emergency evacuation following an earthquake, so should be designed a s "key element".
Conclusion - a combination of modelling and engineering judgement helps - give the staircase slabs maximum attention - rest is often luck.