Max Percentage of steel in Columns
Osama Anwar
Assalaam o Alliakum Everyone,
I know max percentage of steel in column is 4%. But I would like to ask that would you decrease the cross section of your column (considering rebar area doesn't change much) to the extent that it reaches 4%? We know that decreasing the cross section would cause an increase in steel percentage (e.g. 1in^2 Ast in 10"x10" column means 1% steel, but 1in^2 Ast in 8"x8" column means 1.5625% steel). Moreover, in my case the increase in steel is only required to satisfy 6/5 beam/column capacity ratio present in 1st story all columns are passing for flexure. Would you decrease cross section to the extent that steel % is 4% in a column or not? I know you are allowed to increase steel % up to 4% but if the site is in Pakistan then you have to consider steel congestion and workmanship. To which max threshold we generally increase steel %, 2%, 3% or 4%?
Salam Osama,
Increasing reinf in columns or RCC members compromise ductility, it is not good to increase the steel to 4%. when you will use the 4% in column section, what will be the %age at lap?8%. Contractors and architects normally insist to decrease the column sizes but SE must consider the ductility and should not consider them blindly.
  • 4 weeks later...
use staggered bar detailing at lap joint , by doing this , you can provide 5.25% steel in column instead of 4%, at lap joint column steel from above story will be half , so total steel at lap will be 5.25+5.25/2= 7.875% , which is less than 8% for IMRF . This detailed not applied to SMRF , as code restricted max column steel < 6%
@kHURRAM ALImakes a good point about staggered laps. Staggered laps are a good practice on columns, beams, walls and slab.
1. The reinforcement arrangement should be always be staggered to avoid, or reduce likelihood of large cracks or spalling.
2. The staggered laps should not be located in areas of high moment.
This is what Eurocode EC2 guidance is for column - 4% max generally, to 8% max at laps (although this is always less in reality by staggered laps) . Columns have to be designed to be ductile and hence  limits apply. The concrete takes compression load, whilst reinforcement takes tensile loads. In slender columns the failure is most case is due to bending.
Therefore best to stagger laps for better performance. There is a technical reason behind these max limits so best to work within them, otherwise also difficult to prove otherwise to checking engineers and authorities.