Steel Material testing number
callmeismail
Assalamu alaikum,
This question is more of Testing than Designing Steel structure.
Say, someone is fabricating a structure as per design structural drawing. The owner wants to know how many tests need to be done for each type of member, say Rafter, Column, Bracing etc. and from where (web, flange etc.) and how many samples are in a test.
Does AISC or any other relevant code prescribe Number of tests to be done to ensure Quality Control? I hope i could make my question clear.
It is normal practice to test 10% of welds by NDT (Non-Destructive Testing).
This could be either by Magnet Particle Testing (MT) or Ultrasonic Testing (UT). MT is good for structural steel as the steel has magnetic properties to allow this.
All welds for structural elements should to be undertaken by trained and competent welder.
These welders are trained and tested (certainly in Europe & US, not so in South Asia i find),  and their work is checked regularly by Non-Destructive Testing (NDT) - i.e. visual inspection by someone who understands all aspects of welding, and is probably an experienced Welder who has re-trained to become a Weld Inspector., and is familiar with possible weld defects.
Destructive Testing (DT) which is undertaken on samples, and inspected microscopically, is done on sample pieces only, and verifies the welders compentencies etc.
In most building projects non-destructive testing (NDT) is undertaken:
1.  The welder cleans and visually inspect his own welding;
2. Welding Inspector (QA) inspects all critical welds by visual inspection - 10% of critical members - say connections with high moments and tensile forces.
3. Standards: British (BS), European (EN), International (ISO) Standards:
a. BS EN ISO 17640:2017 - NDT  testing of Welds:
This is the international standard for manual ultrasonic testing of fusion-welded joints in metallic materials thicker than or equal to 8mm which exhibit low ultrasonic attenuation.
The standard’s guidelines detail specific testing techniques for metals that show weakened ultrasonic levels at temperatures of up to 60⁰C. It’s primarily designed for full penetration weld joints where both the welded and parent material are ferritic.
b. BS EN ISO 5817 Welding:
BS EN ISO 5817 is an international welding standard that provides guidelines on quality levels of imperfections in fusion-welded joints (except for beam welding) in all types of steel, nickel, titanium and their alloys.
The purpose of this standard is to define dimensions of typical imperfections which might be expected in normal fabrication of fusion welded joints. It provides three sets of dimensional values to apply to a wide range of welded fabrication. They are designated by symbols B, C and D. Quality level B corresponds to the highest requirement on the finished weld. Several types of loads are considered, e.g. static load, thermal load, corrosion load, pressure load. The quality levels refer to production and good workmanship.
BS EN ISO 5817 applies to joints with a material thickness ≥ 0,5 mm. It covers fully penetrated butt welds and all fillet welds. Its principles can also be applied to partial-penetration butt welds.
Thanks SimpleStructure. What you siad is all about weldings, and pretty in depth, i appreciate it.
But what about structural members plate testing? Does the Owner need to test certain amount of samples to valiadte strength of materails?
Where I am working, all steelwork (structural steelwork sections & reinforcement for rc) come with manufacturer’s test certificates etc. This verifies the structural grades. You can trust the paperwork.
For structural steelwork the design code BS EN 1993-1-1 (Eurocode EC3) uses 235 N/mm² and 460 N/mm² steel grades in accordance with the following standards:
1.    BS EN 10025-2: 2019, Hot rolled products of structural steels.
2.    BS EN 10210-1: 2006, Hot finished structural hollow sections of non-alloy and fine grain steels.
3.    BS EN 10219-1: 2006, Cold formed welded structural hollow sections of non-alloy and fine grain steels.
Okay, I understand. So it implies that Material properties may be trusted based on Fabricator's test reports but connection welds need to be inspected to verify proper strength. is it so?
1. Material properties from Manufacturer/Supplier of steelwork section, i.e Steel Mill. This information is trusted in the West (however, in South Asia, just double check that the certificate is genuine)
2. Welding and connections verification /certification by Fabricator or the testing Company he has used, if independent checks are done.
  • 4 weeks later...
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik