Cracked Section Requirement in Etabs
Rifat
Assalamu alikum all,
I have two query about performing equivalent static analysis in Etabs. When we perform equivalent static analysis in Etabs, is it require to perform it in cracked section frames? If we are interested to perform P-Δ analysis, cracked section is required, but if we are not interested to perform P-Δ analysis, then is cracked section required?
My second query is for compatibility torsion in a beam, what is the rules for reducing torsional value in Etabs? Can we nullify full torsion in these beam (0.001) or can we reduce some torsion (e.g. say 0.5 or 0.25) in these beam?
Sorry for my bad English,thanks in advanced.
Yes, you not need to consider the effect of cracking in sections. Following is an excerpt from ASCE/SEI 7-16
"A mathematical model of the structure shall be constructed for the purpose of determining
member forces and structure displacements resulting from applied loads and any imposed displacements or P-delta
effects. The model shall include the stiffness and strength of elements that are signi
fi
cant to the distribution of forces and
deformations in the structure and represent the spatial distribution of mass and stiffness throughout the structure.
In addition, the model shall comply with the following:
a. Stiffness properties of concrete and masonry elements shall consider the effects of cracked sections."
ACI 318, or equivalent guidelines, set the rules. Use manual calculations/excel sheet to investigate your beams. A single modifier can not be applicable to every x-section of beam. It better to use a low modifier for all beams (0.1 or 0.01), and then manually verify only those cross-sections who are failing the shear+torsion interaction as per results of ETABS.
Jazakallah khairan. Thanks for reply.
That means if we are not wish to calculate P-delta effects in our structures,I can neglect cracked section.
I can not reduce torsion modifier in a single beam? After manual calculation if I get some of beam I can neglect torsion and some of beam I have to count full torsion,that what can I do? What procedure do you follow in structural design practicing office?
Thanks in advanced
You got it all wrong. You have to consider cracked sections in your analysis irrespective of the need for the inclusion of P-delta effects.
If it is the case of compatibility torsion, then you don't need to consider full torsion.