Electric/ Signal Pole foundation design guideline
hani
I am working on the design of signal pole. I need to kwon about the resistive moment of the pole. The foundation is 18"X18" and 6' deep. The resistive moment is the weight times the half width of foundation. i need to know another resistive factor on this foundation. that is the passive pressure of the soil on foundation. what is the procedure to calculate the soil pressure on foundation.
hani,
Looks like your pole foundation is a shallow (isolated) foundation resting on grade. First you need to calculate the applied loads at top of pedestal on which your pole is sitting. Then you need to check the foundation size to make sure the overturning and sliding of foundation is within the allowable limits based on the code that you are following. This will include a check in which you will check the compression/ tension couple in foundation and to make sure eccentricity is not large so that you foundation is not in tension. Such checks are provided in standard hand books. For passive pressure, see what your geotech report says. Normal practice is to ignore it.
Thank u sir for your kind response. Sir i need to understand the concept of electric poles that has no isolated foundation and only embedded in soil up to 4-5ft. the overturning moment is resisted by the passive pressure of the soil only.
Hani,
The embedment looks shallow for such case as it takes a lot of structure movement to mobilize “passive soil resistance”. Your pole might have tilted by then - a serviceability failure.
I mean look at nature, the taller the tree, the deeper the roots. Same goes for mountains. Generally it is said that the height the mountain extends above ground, the same footprint is present inside the ground too. For such case, you are better off to provide pile(s) under poles.
Shallow embedment is also tricky as top soil layer can be subjected to frost, adfreeze, erosion, soil run off etc. I would provide a pile and design accordingly. How tall are the poles for which you are providing this solution?
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik