12 hours ago, waqar saleem said:
Salam,
I have a raft modeled in Safe based on Etabs, edges show too high stresses and soil pressure, i have reasonable offset from the column grids. How i could resolve this issue.
Thank you in Advance.
Waqar,
You can change your column framing by adding more columns so load on edge columns is smaller than what you have now. Also review your load input and sharpen the pencil to see if there is any conservatism in the loads and take them out.
Whilst waiting for Waqar's response, here are my thoughts:
It is common for geotechnical engineers to allow 20% overstress on bearing pressure due to transient (non-permanent) loading, i.e wind.
For allowing 20% overstress of bearing pressures due to dead and superimposed live loading, I would expect the concrete raft to be stiffened along the edges (edge thickening) to assist with the spread over a wider area, and thus averaged out in terms of allowable soil bearing pressure and settlement?
With 20% overstress there will be rotation along the raft edges too - that needs to be a design consideration.
Also edges of rafts may be subject to erosion or softening of soil from say someone laying a draining pipe along the edge of the raft, or digging an excavation adjacent to the edge of the raft. Think in terms of building foundation performance - over its 50+ years life!
The figure below is quiet interesting on simple pad footing case, and how pressure distributes under s a pad (sort of a raft), depending on soil type.
Always good to get a geotechnical engineer's opinion on soil bearing pressure matters.
Excellent reply here. Just to add that this is allowed in some code and not allowed in others for Transient Loading (temporary like Seismic and Wind). Not sure what is the basis for Waqar's design but he can confirm and check with geotech if he can use the extra 20 or 30 percent.
Thank you All,
@UmarMakhzumi, building is in islamabad area. I tried with geotech but its unfortunate i could nt get much support, i approached some geotech firms around but every geotech has its own logics and ram leela.
@Simple Structures thank you very much for an elaborate reply.
On 11/16/2020 at 5:37 PM, Ayesha said:
What is the basis for this statement?
some of the basis is shared by Umar and Simple, and some study of subgrade reaction which depends on settlement in the denominator, towards edges settlement decreases and subgrade increases. Dont have any exact basis but some engineering judgement.
Waqar,
One thing that comes to my mind is that if there is a possibility to have another building being constructed adjacent to yours. By adjacent I mean side by side. The can probably result in some excessive settlement down the road. Just a thought.
Edited by UmarMakhzumi
Fixed typos!
Please find the pages from "Design application of Raft foundation by J.A. Hemsley". He is recommending to increase the stiffness of outermost springs to be increased.
By how much increase don't mentioned. If anyone has this complete book may please share.
Pages from jahemsley design applications of raft foundations.pdf