Short term (cracked) deflection for cantilever slab in SAFE
Thila
Hi All,
How to perform analysis to check Short term (cracked) deflection for cantilever in SAFE model?
I have to check for wind load alone. I entered "0" for material unit weight, since i consider only wind pressure. Also in Load case option, I selected "Non- LInear (cracked)" alone. I applied wind pressure of 1.1 kn/m2 for 2.5 m length of slab whereas the total length of slab is 3.5 m. Kindly find attached for geometry.
Is this the right approach?
why am I getting different result comparing to manual calculation? I have attached the SAFE model too.
se-SAFE- defl chk.$sf se-SAFE- defl chk.FDB
Hi, Thank you for your response.
Self weight is ignored since calculation only for wind load.
Manual calculations are as follows:
 l                                   1.1 kN/m
 l________________mmmmmmmmmmmmm
 l
 l---0.85m-----l- ---2.5 m--------------l
 l-------------------3.35 m-------------l
B = 1000 mm
D = 120mm
Ig = 1000 x 1203 / 12 = 144x106 mm4
n = Es/Ec = 200000/ 26587 = 7.52
Fr = 0.62 SQRT (32) = 3.56 N/mm2
Yt = 120/2 = 60 mm
Mcr = Fr*Ig/ yt = 3.56 *144x106 / 60 = 8.544 kNm
Ma = 5.775 kNm
Ma/Mcr <1, Hence Ie = Ig
Deflection = w (uniformly distributed) *l3 / 8*E*Ig
w = 1.1 kN/m = 1.1 n/mm
loaded length = 2500 mm
total length = 3350 mm
E = 26587 N/ mm2
Ig = 144 x 106 mm4
Deflection = 1.1 * 3500*3500* 3500 / 8 * 26587 * 144x 106
                    = 0.0015 mm
I posted the SAFE model snapshot also for your review.
To satisfy the overturning and sliding, 1.0m x 1.2m footing size is enough. But just because of this deflection criteria, footing size and also the thickness of wall increases.
Also is there any reference for short term (cracked ) limit horizontal displacement
7 hours ago, Thila said:
Thank you. But is this correct concept to check the boundary wall deflection in this way without considering the soil load above footing.
If you are taking about adding the deflection due to lateral pressure of soil above the footing pad, it will have negligible contribution.
I am not aware of it.
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik