Beam Moment Release in RCC Frame
Ali Shan
I have a 3 story RCC Frame. During construction phase, it was revealed that columns of the frame were under-designed (provided reinforcement is 3% and required is 4.2%. Columns have been constructed upto first slab level and beams/slabs have not been laid yet.
We are thinking to redesign the frame by releasing moments at ends of RCC beams (which have not been laid yet) so that moments in columns can be minimised and the previously provided 3% steel in columns may become sufficient.
Is the approach of releasing beam end moments in RCC Frame (with monolithic beam to column joints) correct??
How we will detail the joint? What will be the degree of cracking at joints when beam ends will rotate??
Has anyone ever experienced such deign?
Hi Ali,
End release is not preferred in concrete elements since it will require to allow for some cracks on beams and also difficult to detail in drawings
Releasing frames may touch the stability also of the lateral framing system unless you have another existing system cover this.
You may design column as flexure member by adding localized reinforcement covering moment only from one side and can be developed from one side to the beam/slab
This is an interesting situation.
I also agree with @Ebeid that releasing beams wouldn't be a wise thing to do as it will also effect lateral force resisting system.
The frist thing that I would suggest would be to sharpen the pencil and see if the loads have any contingency and remove that contingency from loads and checking if the provided reinforcement in the column works.
If that doesn't work, you can add more columns per bay to make things work but it would require new foundations.
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik