Design of Edge Strip footing.
abbaskhan2294
I have a question related to design of edge strip footing. Below is the sketch for illustration.
The footing to be designed is a strip footing that is going to support a brick masonry wall on top. The literature on every footing design suggests that the resultant load should act within kern of the footing and if its outside the kern then increase the width and that's pretty much it.
However in practice for edge strip footings the perpendicular strips are reinforced with negative reinforcement for preventing the overturning of the footing and as a result the uniform stresses distribution in soil is achieve and differential settlement/overturning is prevented.
Here in my case, the building is erected from basement and the finish floor level is 4 ft above the NSL. The foundation of only one load bearing wall is to be erected 3 ft below NSL and in such case no perpendicular strips are available to prevent the overturning as they are erected below the basement level. What's your take on this? I believe if a footing is designed rigidly it will have the tendency of uniform stresses distribution in soil and will not cause overturning. Please provide your opinion on this as this is one common issue in design practice.
Edited by abbaskhan2294
Could you share complete plan of building and a section .you may add some piles under foundation of wall to stabilize it or connect wall foundation with upper level foundation through beams or strips connected through a cut off wall.
Well I got a few solutions for the problems and I will list them below:
1- providing tie down anchor on the right extreme end of the footing.
2- projecting footing of the edge wall in L shape at the tension end to provide firm support through length of the wall.
3- Rather then starting the wall in masonry right from footing , cast the wall in RCC to plinth level and protruding reinforcement in the slab to resist the overturning.
4- providing perpendicular strip footings and designing it for negative reinforcement to resist the overturning of the adjacent Edge wall footing.
out of these all #3 and #4 were found to be the best solution in terms of cost saving. Please add your comments too. Regards
Abbas,
The literature is clear, if it is outside, it is unstable. You need to make it inside or equilibrium won't hold.
Negative reinforcement will design the slab to take the moment but the "geometric sizing" will prevent overturning. Presence of reinforcement doesn't add to stability.
Simplest solution would be move the wall inside and use backfill to counterbalance any overturning. Other solutions can be pouring a raft.
Hope that helps.
The solution in the sketch is pretty straight forward but none of the clients will agree to this solution as he would be losing his valuable space.
Also, In order to avoid any tension you can also not go into the property line of others as it would either lead to damage of their structure or yours in future during excavation procedures.
I believe perpendicular strips designed for flexural can control the overturning provided the you have enough development length for transfer of moments to adjacent perpendicular strips. The mechanism would be that the torsion (overturning) in the edge wall footing shall be transferred as moment in the perpendicular strips and the reinforcement provided on fully development will prevent the overturning of the edge footing.
The kern check is the stability check for foundation. Failing that means limit state failure. Other options would be doing piling or tie the foundation using a beam to next available foundation and design accordingly.
Edited by Ayesha