I found this statement on quora " If the live load is greater than 5 KN/m2 (105 lb/ft2) then 50% of live load is considered in Mass source". It was quoted according to Indian code, but I couldn't find anything related this in ACI. Can anyone explain this ?
and Also should we base P-Delta analysis on Mass or loads. I read CSI details on this, where they mentioned if gravity loads are specified then it is recommended to use iterative. I cannot get firm clarification. kindly explain
By ACI, I reckon you are referring to the ACI 318 document.
That document primarily lays out guidelines for safe construction and design of some of the reinforced concrete structures. That document does not give guidelines to calculate wind, seismic, or other kind of forces.
For these guidelines, you need to consult IBC, UBC, or ASCE7 documents.
The inclusion of live load in seismic weight is laid out differently in US-based codes.
Following are the statements from UBC 97 (Section 1630.1.1):
Seismic dead load, W, is the total dead load and applicable portions of other loads listed below.
1. In storage and warehouse occupancies, a minimum of 25 percent of the floor live load shall be applicable.
2. Where a partition load is used in the floor design, a load of not less than 10 psf (0.48 kN/m2) shall be included.
3. Design snow loads of 30 psf (1.44 kN/m2) or less need not be included. Where design snow loads exceed 30 psf (1.44 kN/m2), the design snow load shall be included, but may be reduced up to 75 percent where consideration of siting, configuration and load duration warrant when approved by the building official.
4. Total weight of permanent equipment shall be included.
Following are the statements from ASCE7-22 ( Section 12.7.2):
1. In areas used for storage, a minimum of 25% of the floor live load shall be included.
2. Where provision for partitions is made or where required by Section 4.3.2 in the floor load design, the actual partition weight or a minimum weight of 10 lb/ft2 (0.48 kN/m2) of floor area, whichever is greater.
3. Total operating weight of permanent equipment.
4. Where the flat roof snow load, Pf , exceeds 45 lb/ft2 (2.16 kN/m2), 15% of the uniform design snow load, regardless of actual roof slope.
5. Weight of landscaping and other materials at roof gardens and similar areas, as defined in Section 3.1.4.
6. Weight of fluids and bulk material expected to be present during normal use.
We usually model our structures in a way that lets as assign all the relevant loads on the structural model through line loads and area loads. And we usually divide gravity loads into three or more categories.
For P-delta analysis, the program needs the source of gravity loads acting on the deformed state of structure. Since we already had defined those in the form of load patterns, it is convenient to use load based option.
For mass based P-delta, the programme (ETABs) says: This is an approximate method which does not require an iterative solution, providing for faster computation. P-Delta is considered by treating the structure as a simplified stick model, a process which is most effective with a single rigid diaphragm at each level. Local buckling is not captured as effectively.