High strength Concrete
Dear Colleagues,
Salam, i have a high strength concrete on a project specified C90/105, it is around 13ksi, concrete has some irregular cracks on top and bottom both sides, concrete depth is 1m and it has 4 layers of reinforcement D32@150 both sides. I checked the design mix trial tests, it is achieving 87.5Mpa in just three days, is it right? mix design has 1.5 air entrainment, what is the purpose of this? normally we compact and reduce voids, concrete is also self compacting, is it possible for a SCC to entrain some air?
Thank You
I assume your mix design is 90 MPa concrete (@28 days).  I don't know what the concrete object that has the cracking is. For that strength gain, there is likely a very small portion of fly-ash, so there is likely a lot of cement powder.  What is the size of your aggregate; you could have a lot of shrinkage. 1.5% air is not unusual. You can have that amount with normal mixing.  This is normally less than 1%. In our environs exterior  concrete usually has about 6% or 7% for frost resistance. A lot of our concrete has fly-ash for economy.  I've not used self compacting concrete, but have often spec'd superplasticisers. I always spec mechanical vibration, even for piles and caissons.
Dik
Thank You Dik, Slab has cracks, its 1000mm thick, and in octagonal shape, please see the document attached, its an initial draft. Mix design is also attached.
@Badar (BAZ) @UmarMakhzumi Kindly have a look.
Initital report for foundation cracks.pdf Mix design C-90 105.pdf
I am not in a position to comment on the part related to properties of concrete.
There can be number of reasons for it. Shrinkage is most obvious one. Do they have reasonable spacing of temp and shrinkage rebars, if any?
Are cracks wide enough to lead to yielding in rebars?
Have you established the structural adequacy to eliminate the possibility of structural cracks?
Salam, Thank you Badar, thickness is 1000mm and it has 4 layers of Dia 32 rebars in both directions, and a smaller size mesh at the top also of Dia 16, my perception is also of temp/shrinkage cracks, I collected the data, first crack appeared one week after pouring of concrete, cracks continue to appear and randomly, scanned and depth is 18cm at top and 10com at the bottom, at top cover is 8 cm, i dont understand why this much cover is provided.
Dear Waqar
please check the pouring methodology and measures adopted to control temperature for mass concreting, if any. Then you can calculate the temperature rise during hardening of concrete and compare the difference of atmospheric temperature and concrete temperature. As very high cement content is anticipated so stringent temperature control requirements should have been adopted. By this you would be able to figure out whether these are temperature shrinkage cracks or otherwise. Moreover please calculate the crack width. As cover is high therefore there is a possibility that you may end up in calculating the crack width equivalent to whatever is visible there in the slab.  Pattern of cracks you highlighted indicates the temperature shrinkage nature of cracks however calculations are needed to confirm the anticipation.
Dear Imran sb, Thank You, very much, we are on it. Slab is octagonal and pouring is done 4 portions first and then a gap and 4 are poured, temp is monitored by embedded sensor and readings are okay, a canopy is set above the slab and heaters are placed to maintain the temperature difference normal, scanning results are received, 50 readings, top/bottom 25/25, 50 percent are crossing into the core area or below the top bar, mostly are top side cracks, crack depths are max 20cm, cover to top rebar is 8cm. one thing i observed that mix design recommends 3 days strength 60/90 but in actual testing it is 87/90 in 3 days, rate of hydration is more then recommended or observed during trial mixes, please some data/example to calculate crack widths. Thank You
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik