33 % Increase In Bearing Capacity In Transient Load Condition
Muhammad Hassan
There are 2 things..
First, the 1/3 rd stress increase for soil pressures shouldn't be taken for granted, and shall only be be used after due consultation with the geotechnical engineer. I dont have a code reference for 33% thing but if It isn't mentioned in the code, it is commonly allowed by the Geotech engineer. The following note is from the geotech report for a current project. "The net allowable bearing pressure may be increased by one-third for transient wind or seismic loads."
Second,
Another possible alternative would be to reduce forces and have a economical design ,
The 25% reduction applied to the overall overturning moment at the base of the structure due to lateral seismic forces (talking about the big picture here - not moment on an individual footing). As the structure overturning moment is generally resolved into a force couple in braced frames or individual moments in footings, I read this as allowing a reduction in either the force couple or the individual moments for design, both strength and stability, of the footings.
As basis see the 2009 NEHRP Provisions which basically provide a commentary to ASCE 7-2005 (downloadable - big file - here: http://www.fema.gov/...cord.do?id=4103) which says for this provision (emphasis added):
C12.13.4 Reduction of Foundation Overturning. Since the vertical distribution of forces prescribed for use with the
equivalent lateral force procedure is intended to envelope story shears, overturning moments are exaggerated. (See
Section C12.13.3.) Such moments will be lower where multiple modes respond, so a 25 percent reduction is permitted for
design (strength and stability) of the foundation using this procedure.
Note:This 25% reduction is for seismic only.
Edited by Umar Makhzumi
Note added
i was making load combinations for descon new project. it was strange when i found out they are unaware of vertical component of earthquake. Except one project they don't take this. further more they are also unaware of special seismic combinations.
but one thing is encouraging tht they most deal with steel structures and when we use ASD Ev is zero. This clause has saved them till yet
Sir umer i had studied this document before starting discussion. This mainly adresses the stress increase in structural materials. This was practice followed before 1990's because at that time factor of 0.75 was not introduced in load combinations. We can increase allowable bearing capacity of soil by 33% under eartquake and wind conditions.
soil is the material with most unpredictable behaviour and without any strongly recommended reference it is not reasonable to increase the capacity , yes you are right!!!let the blame going to others typical approach :P
  • 2 years later...
What I have concluded after reading above posts and documents, is that
1) The 1/3d increase in stress by ASD method may be either due to
i) loading rate
ii) loading duration
iii) some other such reason based on engineering judgement
iV) And most importantly due the reason that when two transient loads (loads having tendency to vary in magnitude with respect to time e.g. live, earth quack, wind etc)  act simultaneously on a structure, then one transient load acts as full value load and other structure has less probability of occurrence. So it is not fair to combine these two transient loads at their full value loads. So both of the transient loads are either allowed to reduce upto some extent (As codes specify 25% reduction in transient loads) OR corresponding stress in material is increased by 33%.
(Note that 0.75 is reduction factor for transient simultaneously acting loads and reciprocal of 0.75 i.e. 1/0.75 = 1.33 i.e. increment factor of stress. )
Basic equation of equilibrium is
Loads = Stress
In case of simultaneously acting transient loads,
either you can do
0.75*loads = stress
OR
Loads = stress/0.75 = 1.33*stress
But keep in mind that since this stress increment is due to the fact that both transient loads can not act simultaneously at their full value so we are reducing loads or increasing stress. This stress increment has nothing to do with DEAD LOADS. So we can not reduce dead load and this factor of 0.75 is applied only to transient loads.
You can find in different codes in practice two types of load combinations.
Basic and Alternate.
One type of load combinations include this 0.75 reduction factor in them so using these types of load combinations we can not increase stress. because reducing loads for the same reason and increasing stress for again the same reason SIMULTANEOUSLY is UNSAFE. You can go for one approach at a time.
More over, Codes also say that the effect due to load combination carrying two or more transient loads with reduced values must not be less than the effect of only one (most severe) transient load acting at full value.
The document presented by Sir Umer clearly says that this stress increment should not be taken even in case of earth quack loads if 0.75 reduction factor has been already used in load combinations.
More over, in sizing of footing, we go for ASD approach because bearing capacity given by geotechnical engineer is based on the concept that full factor of safety of 2-3 is applied on soil strength and no loads are increased. This is ASD methodology. So to be compatible, we also go for ASD while sizing of foundation. So in my opinion, if you are using load combinations which are carrying 0.75 reduction factor, you can not increase soil stress by 33% even not for earth quack loads. but if you are using the load combinations which are not having 0.75 reduction, then you can increase this stress as 33% but just for those cases where two or more than two transient loads are acting simultaneously.
There are two noticeable references mentioned in this thread.
One is specific to Load Combinations(ASD stuff) and subsequent 1/3rd reduction, the other is about C12.13.4 of ASCE 7-05: 25% reduction of seismic overturning moment for the case of Equivalent Static Lateral Force Procedure. For some reason, all the replies have been focused on ASD Load Combinations and subsequent 1/3rd reduction. Anyways, ASD is old in a matter of few years would be completely wiped out of the scene for foundations. The current practice in industry is to use LRFD for foundation design. Moreover, make sure you touch base with the Geotechnical Engineer.  Sometimes geotech reports specify what could be done or not with regards to thread subject.
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik