Safe Punching Shear Problem
m_naeem_b
when ever I draw model on safe v.8. If punching shear ratio of raft foundation exceed. for example: If punching ratio of column on raft foundation 30" thick is 1.6, then I draw an other 10'x10' slab with same property in 30" thick raft with 33" on that particular column which have punching ratio 1.6. It wil come to 1.3 punching ratio.. then 36" and 39", after that punching ratio will come below 1.
But when ever I remove 30" thick raft on that column then draw only 39" thick raft, i am facing same punching ratio problem. I did'nt understand what criteria SAFE is following..
Well in SAFE the punching area is calculated based on the column or load size. When you are not placing any stiff section on the column center or the load size is not defined then you punchign area is reduced giving you more reinforcement. So when you put the right column or load size it gives you correct values of the punching!
He is right. Moreover, Never follow safe blindly. Punching shear is the easiest to calculate, just do manual checks.
i am also having problem in punching shear ratio, SAFE gives very large values as compared to manual calculations..e.g i have column load of 6189 kips SAFE is giving value of 1.28 but manually it is 0.94...
Have you checked what load combo SAFE determines as max for punching and checked your values manually against that combo? I am saying this because, due to seismic, you can have large compression on columns, and manual check we do is mostly for 1.2D + 1.6L
well i dont believe SAFE gives wrong results as compared with manual calculations.. and here im talking about SAFE 12
But you have to consider following things:-
1) check the load size for perimeter calculation
2) apply the correct parameter for location of column...For example if it is interior column , select the point goto Design>Punhcing Overwrites and make it interior
3) Make correct cover settings. Goto Design> Design Preferences and put the correct cover and bar size
4) Make sure you are familiar with the load combos for which you will design your structure or punching
After analysis, right click on the point of column you will see detailed calculations for punching and the governing combination. Make sure SAFE 12 is calculating the effective depth and the perimeter correct which will surely be correct if you follow above steps. You can also check punching calculations of other non governing combinations.
i removed all the earthquake combos and with only two combos i checked the results and thier is a variation in values also...i am unable to upload the sheets otherwise i can show u the maual as well as SAFE results..
did u take care of all the points i mentioned above?
I didn't use SAFE 12. I am talking about SAFE v.8. I want to ask that on 30" thick raft foundation, can we place 39" thick drop on it?
if I remove 30" and place only 39" then again punching increase by 1 also soil pressure increases.?
Look what i understood from your question is that
In SAFE 8
1) when you make 30" thick raft it gives you punching ratio more than 1. bcz 30" may not be adequate for your loads
2) when you make 39" thick raft (drop) on already placed 30" raft. It gives your value greater than 1 because, still the perimeter may not be adequate and thcikness may not be ok! tell me the loads
3) When you make 30" and 39" overlapping each other they dont make 30+39, rather they the largest of them is used for caluclation.
4) In SAFE 8 there is also an option for the location, and cover and bar size data. You must have to prvide that data to get the desired results!
if i put a slab beneath a slab and by assigning it soil support means to reduce the soil pressure under that area...you can chk it by simply putting two slabs over each other...and here in some design offices people use 4 in thk lean beneath foundation in SAFE and it reduces the soil pressure but they are keep on doing this i argue this matter with different peoples but they think they are doing it right....
You should never model lean as its not a part of foundation system. It is similar to considering plaster on slabs acting as part of slab and contributing to strength of slab.
lean should never model... if you read from it from manual of safe or somewhere else.. kindly share with us....
It isnt from any manual but its straight forward. How can you justify added strength due to lean?
Do you know why lean is provided?
Look you can not model each and every thing in your structural software...Yes you can for research purposed but for practical purposes you should never because:-
1) It takes time and not practicle in tight schedules and dead lines
2) the affect of it might be less than only 1%
3) keep the things simple to understand for reviewing team and for your self too
There are many assumptions, things we base our calculations on those. Many things we ignore and many we assume. Its engineering!
I would recommend you to not model lean, as sir Umar said not model plaster and so on!
Be a structural guy! :P