Live Load Reduction
m_naeem_b
If you specify reducible live load in static load cases then it will apply live load reduction based on OPTIONS>PREFERENCES>LIVE LOAD REDUCTION parameters.
If you apply only normal LIVE load cases then the live load reduction will not have any affect on this!
I did not got ur point... how it applies ? and what are the condition?
In my point of view there is no link b/w reducible live load "in preference option" and reducible live load "in static load cases".?
You can read conditions in which we may reduce live loads in attached document. When you will select reduceable live load in software, it will automatically reduce the live load according to the Code.
It is economical and logical to reduce live load in certain cases,read attached doc, because probability of occurrance of full live load in all floors at same time is very less. (see section 4.8)
http://dl.dropbox.co... loads -s04.pdf
Judgement should also be considered other to what code says.
Never Use LLR for Marriage Halls. Just a tip! :)
Well! codes we use are based on American culture. Surely they don't celebrate marriages as we do. :)
Even if marriage hall has three or four floors, I have seen occasions in which 3/4 marriage ceremonies taking place at same time.
In US, I have seen classrooms, that have a capacity limit. Max 45 people.
it depends. (common sense) if you building is the building containing lot of fluids (may be in case of some industrial water buildings) then yes...but if it is just a small water tank at top then no....anyways you can conservatively include this as live load...because only upto 25% of LL is considerderd in MASS SOURCE...and Dead Loads are always much more than LL....so it will not make a huge difference.. Generally LIVE LOAD portion (25% of LL in MASS SOURCE) is less than 10% of total sesimc weight!
For example if all the
DEAD LOADS = 25000 kN
LIVE LOADS = 10000 kN
MASS SOURCE = 100%D + 25% L = 25k KN + 2.5k KN = 27.5kN
Live load portion is 2.5/27.5 = 9 % approx
  • 5 years later...
Dwar Baz in the above link file not found.we usually select Tributary Area for L.L.R,can sm1 explain why its done and wat abt other options like Influence area etc.thnx
The file referred in the link is Chapter 4 of 2002 version (ASCE 7-02) of 'Minimum Design Loads for Buildings and Other Structures', dealing with Live Loads. Reduction of Live Load is permitted, as per procedure & limitations described in Section 4.8 of this chapter.
This information is also available in later versions of ASCE 7. In case of ASCE 7-05, it is provided in Section 4.8, whereas in ASCE 7-10, you may find it in Section 4.7 of the standard.
  • 3 months later...
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik