Diaphragm
jammer3425
what is the purpose of assigning diaphragm b4 running analysis of concrete structure in ETABS and what type of diaphragm is required to be assigned to the structure as it shows us two types rigid and semi rigid. what role does these factors governs or play in the design of the structure?
Diaphragms connect all individual members into a seismic force resisting system. If you have concrete floors, it is imperative that your floor will do the above mentioned job plus distribute the seismic load to all the connecting members too.
Diaphragms can be rigid or flexible depending upon their stiffness. For practise in Pakistan, if your flooring is type conc slab > 5" consider your diaphragm to be rigid. A rigid diaphragm distributes forces to connecting members based on connecting members stiffness, where as a flexible diaphragm distributes loading based on tributary areas of supporting members to diaphragm. Take diaphragm as a frame that connects all members, and makes them act together.
Here, My fav on diaphargms
Diaphragm behavior and idealizations
All frames equal stiffness
Symmetrically arranged & equal stiffness means equal resistance Under the rigid diaphragm idealization, the symmetrically arranged identical frames experience the same deflection, and provide equal resistance.
Third frame is twice as stiff
Concrete slab
Sir what difference would it make if we dont assign diaphragm in ETABS?
I havent tried it but I guess Etabs wont do any calcs related to seismic distribution. Also, center of mass and rigitity calculations are purley based on diaphragm assignment.
  • 5 years later...
  • 4 weeks later...
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik