Different Strengths Of Column And Slab Concrete
WR1
Dear members,
I have different concrete strengths of column and slab and the difference is exactly 40%. I mean col strength is 70mPa and slab strength is 40mPa. 70/40 = 1.40
I am following ACI code, i will quote ACI 10.12 "Transmission of column loads through floor system"
It is written that "if f'c of column is greater than 1.4 times that of the floor system, transmission of load through the floor system shall be provided by 10.12.1, 10.12.2 or 10.12.3."
In these 10.12.1 to 3 concrete placing and determination of strength is addressed.
My question is i have exactly 40% difference...NOT MORE THAN 40%. so can i IGNORE this caluse?
and what is the practical solution you would suggest.
Dear members,
I have different concrete strengths of column and slab and the difference is exactly 40%. I mean col strength is 70mPa and slab strength is 40mPa (50 mPa). 70/50 = 1.40
See commentary for 10.15. I would say since you are @ the threshold, just make sure, joint is detailed properly. No other precaution.
I would also say same as Umar. You don't have to follow code provisions 10.12.1 through 10.12.3 as it for ratio >1.4. As a precautionary measure, you can provide for extra confinement of joint or specify same concrete strength for only joint region,no extension in slab.
Increasing confinement of joint region will be easier than pouring higher strength concrete in joint. :)
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik