Assalam o alaikum.

According to ACI 12.5.2,

development length for fc' = 3000, fy=60000, for normal weight concrete and epoxy less reinforcement, The required development length comes out to be

for #3 = 8.2 inch

for #4 = 10.95 inch

for #6 = 16.42 inch

for #8 = 21.9 inch

 

And if in my case, ACI 12.5.3 is not fulfilled, it means now i have to provide ldh as mentioned above. ldh is STRAIGHT EMBEDMENT LENGTH + RADIUS OF BEND + ONE BAR DIAMETER as shown in figure attached. Now my question is, if in my case, main reinforcement of beam is of #6 and #4, minimum column size required will be 18 inch and 12 inch respectively. Lets say by any means, i can not select #4, #3 bars and size of column where bars are to be terminated is 12 inch, how to fullfil this development length???

post-1702-0-70473600-1420373375_thumb.pn

Share this post


Link to post
Share on other sites

You can use headed reinforcement , see section 12.6.

If you cannot use headed reinforcement, and cannot provide the length of embedment for the development of top bars in tension, then consider this joint as PIN, and re-run the analysis to get the correct distribution of moments in mid span and other continuous support.

Share this post


Link to post
Share on other sites

Baz bhai, If i make ends of beams as pinned, This member will not be able to redistribute moment and will collapse at the formation of only one plastic hinge. so How REDUCED DESIGN LATERAL FORCE will be calculated and applied to this member? And is such type of beam allowed in IMRF or SMRF which needs special requirements for integrity at joints under lateral deformation of structure?

Share this post


Link to post
Share on other sites

It will require two plastic hinges to develop mechanism, as it act as propped beam, and it can still redistribute moment. You are not relying on plastic strength of the structure to carry gravity loads.

If , in a particular frame, your reliability/redundancy factor is less than 1, excluding  the bay which contains propped beam, and your drifts are under control, then you can use a propped beam in one bay of that frame.

If you can afford a non-moment resisting bay, which means your drifts are under control and your structure has adequate redundancy, then you don't have to worry about integrity of that one joint. Other joints and bays of the frame can take care of that.

Share this post


Link to post
Share on other sites

Waqas,

 

First note that development length in indicated case is only the straight length as shown in figure and doesn't include bent portion and secondly this requirement can be fulfilled as follows,

 

1,you can use greater no of lesser dia bars complying ldh requirement and if beam width is insufficient to accommodate greater no of bars then you can distribute them in effective flange width (ACI 318-11 section 10.6.6).

 

2. you can multiply ldh by 0.8 if you tie hooked end reinforcing bar with ties parallel or perpendicular to the bar, spaced not greater than 2db (db = hooked bar diametre).(ACI 318-11 figure R12.5.3).

 

3, You can provide excessive reinforcement and multiply ldh by As req/As prov.

 

4, You can multiply ldh by 0.7 by maintaining minimum side cover to the longitudinal bar to 2.5".

Share this post


Link to post
Share on other sites

Waqas,

 

First note that development length in indicated case is only the straight length as shown in figure and doesn't include bent portion and secondly this requirement can be fulfilled as follows,

 

1,you can use greater no of lesser dia bars complying ldh requirement and if beam width is insufficient to accommodate greater no of bars then you can distribute them in effective flange width (ACI 318-11 section 10.6.6).

 

2. you can multiply ldh by 0.8 if you tie hooked end reinforcing bar with ties parallel or perpendicular to the bar, spaced not greater than 2db (db = hooked bar diametre).(ACI 318-11 figure R12.5.3).

 

3, You can provide excessive reinforcement and multiply ldh by As req/As prov.

 

4, You can multiply ldh by 0.7 by maintaining minimum side cover to the longitudinal bar to 2.5".

Umair bhai, Thanx for your guidance in this regard.

I have gone for option 2  and 4 i.e. I have specified special requirements of concrete covers and have selected reduced development lengths dat fits in my 12 inch column. Regarding you 1st point, i will study it because it unaware of it and it seems very interesting way. Regarding your 3rd point, please explain it. I also cud not understand it from book/Code. Please explain in a bit detail what is it actually and how it works. Thanx.

Share this post


Link to post
Share on other sites

Regarding point # 3, suppose at any support strength requirement shows 3 #6 bars,here to counteract ldh you  provide greater area i.e greater bars for ex if you provide 6 # 6 bars then ldh should be multiplied with As-3#6/As-6#6 i.e 0.5.

 

Concept behind this provision is that if at any support say half ldh is available for stressed bars then these bars will develop half of their strength through bonding in concrete and will be able to take stresses till 0.5xFy,if you add up same no of bars with same ldh then they will also bear stresses upto 0.5xFy and as a whole you will get the required resistance Fy. 

Share this post


Link to post
Share on other sites

Regarding point # 3, suppose at any support strength requirement shows 3 #6 bars,here to counteract ldh you  provide greater area i.e greater bars for ex if you provide 6 # 6 bars then ldh should be multiplied with As-3#6/As-6#6 i.e 0.5.

 

Concept behind this provision is that if at any support say half ldh is available for stressed bars then these bars will develop half of their strength through bonding in concrete and will be able to take stresses till 0.5xFy,if you add up same no of bars with same ldh then they will also bear stresses upto 0.5xFy and as a whole you will get the required resistance Fy. 

This bonding stress comes into existence when the bar experience flexural tension or compression. Now If at support, say negative moment of 50 Kip-ft is to be resisted for which i had provided 3-#6 bars, then this 50 Kip-ft moment will be resisted by these 3 bars and these 3 bars will experience corresponding tension and this tension will become cause of required development length of ldh. Now if i have provided 6 bars. This moment will be resisted by 6 bars and share of moment for each bar will be reduced and each bar now will experience less tension, 50% less than before so now 50% less ldh will also work. Is my understading correct bhai?? Kindly confirm me one thing more. We design each bar for 0.9Fy in LRFD. and for development we provide such development that the bar can experience bond stress upto yield before slippage. so each bar can go upto yielding. But after this reduction of ldh, no matter force experience by each bar not gonna increase than share of each bar, but let say, theoratically now bars can't go beyond 0.5Fy if tried to be stressed more than share on calculation basis and bars will slip just after 0.5Fy. Am i getting right??

and My building is in Quetta for which i have assigned zone 4, SDC E. And PCA Commentry says i can not apply this reduction in Zone 4 SDC E. 

Share this post


Link to post
Share on other sites
PCA Commentry over 12.2.5 is
Quote

 

Reduction in ld may be permitted by the ratio [(As required)/(As provided)] when excess reinforcement is provided in a flexural member.  Note that this reduction does not apply when the full fy development is required, as for tension lap splices in 7.13, 12.15.1, and 13.3.8.5, development of positive moment reinforcement at supports in 12.11.2, and for development of shrinkage and temperature reinforcement according to 7.12.2.3.  Note also that this reduction in development length is not permitted for reinforcement in structures located in regions of high seismic risk or for structures assigned to high seismic performance or design categories (see 21.11.7.3 and R21.11.7.3).

Reduced ld computed after applying the excess reinforcement according to 12.2.5 must not be less than 12 in.....

 

Now i am confused regarding why this is not allowed? Because in those zones we design for reserve strength beyond yield too?? 

 

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now

Sign in to follow this  

  • Our picks

    • I am suppose to design a pile foundation for a machine weighing approximately 50 tons and with an operational loading of 100 tons. 
      I ll appreciate your help in terms of guidance & provision of notes...  
       
      Thank you..
      • 36 replies
    • Material behavior can be idealized as consisting of an 'elastic' domain and a 'plastic' domain. For almost 200 years, structural design has been
      based on an elastic theory which assumes that structures display a linear response throughout their loading history, ignoring the post-yielding
      stage of behavior. Current design practice for reinforced concrete structures is a curious blend of elastic analysis to compute forces and moments, plasticity theory to proportion cross-sections for the moment and axial, load, and empirical mumbo-jumbo to proportion members for shear.

       

      From the book "Design of Concrete Structures with Stress Fields" by A. Muttoni,  J. Schwartz and  B.Thurliman.

       
      • 0 replies
    • Dear Fellow Researchers, Academicians, and research students,

       

      NED University of Engineering & Technology in collaboration with Institution of Engineers Pakistan (IEP) is organizing 9th International Civil Engineering Conference (ICEC 2017) on December 22-23, 2017 at Karachi, Pakistan.

       The congress details are available at its website www.neduet.edu.pk/icec

       Also attached is congress flyer for information and dissemination among your peers.

       Abstracts submission deadline has been extended till October 31, 2017.

      Please click on the link to see the full description.
      • 0 replies
    • AoA all,

      Is it mandatory to do column concreting upto the soffit of the beam in a single pour ?

      What code says about the construction/cold joint location in column ?

      Majority of the contractors are pouring the column concrete upto the soffit of the beam (full height of the column), some contractors leave the column height about 9" to 12" below the beam level and then fill this 9" to 12" column height with the beams & slab concreting. On one site column concreting was stopped at the mid height and the remaining half was filled on the next day.

      Thanks

       

       
      • 5 replies
    • AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       
      • 9 replies
    • Salam Members,

      Congratulations to Engineers, PEC has become full signatory of Washington Accord, what are the benefits to Pakistani engineers for this agreement. 

       

      Regards   

       

       
      • 3 replies
    • Please clarify the following confusions one by one:-

       

      1. If we run P-delta analysis in ETABS, then should we ignore stiffness property modifiers for beams and columns? I have heard that if we perform P-delta analysis and apply stiffness modifiers at the same time then the moment magnification process is doubled...?

       

      2. ETABS considers selenderness of a column by applying moment magnification factors. If we run P-delta analysis also, does it mean that the selenderness of column is being over-estimated? I mean once the moments are magnified in P-delta analysis process and again through moment magnification process?

       

      Please help me understand the software myth and clarify above confusions.
      • 1 reply
    • Assalam o alaikum.
      According to ACI 12.5.2,
      development length for fc' = 3000, fy=60000, for normal weight concrete and epoxy less reinforcement, The required development length comes out to be
      for #3 = 8.2 inch
      for #4 = 10.95 inch
      for #6 = 16.42 inch
      for #8 = 21.9 inch
       
      And if in my case, ACI 12.5.3 is not fulfilled, it means now i have to provide ldh as mentioned above. ldh is STRAIGHT EMBEDMENT LENGTH + RADIUS OF BEND + ONE BAR DIAMETER as shown in figure attached. Now my question is, if in my case, main reinforcement of beam is of #6 and #4, minimum column size required will be 18 inch and 12 inch respectively. Lets say by any means, i can not select #4, #3 bars and size of column where bars are to be terminated is 12 inch, how to fullfil this development length???
      • 11 replies
    • Dear all,

      I am trying to design shearwalls through ETABS with temperature load applied over shell. At various location, spandral section fails in Shear due to temperature and piers (sometime in shear, mostly in flexure).  (See Attached Image)

      Certainly all the problem in Shearwalls are due to temperature. I don't want to increase cross section of spandral or pier at some location just due to temperature load case as it will appears non-uniform with rest of the wall. 

      I have seen stiffness modifier affect distribution of forces and also rigid/semi rigid daiphragm assumption. 

       

      Can anybody guide how to properly design the shear wall with temperature load applied in ETABS or share any similar experience. Thanks in Advance.    
      • 15 replies
    • ENGINEERS;
      I WILL LOOSE MY BRAIN FROM ETABS. 
      I DECIDED TO MAKE MANUAL MESHING FROM AREA ELEMENTS BESIDE EACH OTHER AND EVERY HING WAS FINE .
      BUT AFTER DEVISION SAY 7*7 ELEMNTS FOR EVERY BIG ELEMENT AND MAKING ETABS CHECH..................THEN 500 ERROR MESSAGE THAT ALL ELEMNTS ARE CLOSE TO EACH OTHER.  WHAT ARE GOING...... SOMEONE TELL ME PLEASE...... I WILL LOST MY WORK
      • 6 replies
  • Recently Browsing   0 members

    No registered users viewing this page.

×

Important Information

By using this site, you agree to our Terms of Use and Guidelines.