Unable to print summary report in ETABS

Recommended Posts

Assalam U Alaikum everybody.

Im trying to display the summary report for my model in ETABS 9.7.4 but its giving the error "printing error occured", I printed summary reports of the same model this morning only but its giving this error now, i thought i had made some blunders in the settings so i reverted back to the source file as it was in the morning but its giving the same error, other models reports are being printed. Help would be appreciated

Share this post


Link to post
Share on other sites

1. Import the original text file again.

2. If it doesnt work, assuming you have lateral loads, goto Tables > and show reactions for Ex, Ey ..etc...once the reactions are tabulated. Close and then try again printing the summary report from File menu.

Share this post


Link to post
Share on other sites

The problem was with it printing the reactions and tabulating eccentricity ratios and drift ratios etc within the text file. It would create the text file till T calculations but the rest of the data would be missing after it gave the "printing error occured" dialog.

The only change I was making to the file was that I was changing the stiffness modifiers for the basement retaining wall from 0.01 to 0.0001, except f22 which was left as 0.1. Other than that, I did not change the meshing or anything else. What I dont understand is that how can that cause a problem in it printing the summary report

 

Share this post


Link to post
Share on other sites
17 hours ago, ShamiqSaeed said:

The problem was with it printing the reactions and tabulating eccentricity ratios and drift ratios etc within the text file. It would create the text file till T calculations but the rest of the data would be missing after it gave the "printing error occured" dialog.

The only change I was making to the file was that I was changing the stiffness modifiers for the basement retaining wall from 0.01 to 0.0001, except f22 which was left as 0.1. Other than that, I did not change the meshing or anything else. What I dont understand is that how can that cause a problem in it printing the summary report

 

That shouldn't cause any problem. Try uninstalling and reinstalling ETABS.

Thanks.

 

Share this post


Link to post
Share on other sites
22 hours ago, ShamiqSaeed said:

The only change I was making to the file was that I was changing the stiffness modifiers for the basement retaining wall from 0.01 to 0.0001,

That might have caused some inconsistencies in the calculations (very small/large values) and could have caused this error. There is not much diff in behaviour if you change from 0.01 to 0.0001 so keep the previous value.

5 hours ago, UmarMakhzumi said:

That shouldn't cause any problem. Try uninstalling and reinstalling ETABS.

Thanks.

 

That would not solve the problem i reckon.

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now

  • Our picks

    • Dear All,

      The forum has been updated today with a lot new features.

      You can find the list of all the new improvements by visiting this website.

      Some highlights are:

      1) Improved Search Features


      2) Emoji

      Emoji support is now available in all editors.


      Do check out the link posted above for the complete list.

      One additional announcement that I would like to make is that with reference to last forum update post (read below),  @Rana and @BAZ are forum Admins now. I think it was important to do as it brings more transparency for the forum and also helps spread the responsibility. The forum belongs to the members so it never made sense for one person to be Admin,

      As always, feedback is much appreciated.

      Thanks for taking the time out to read this update.

      Cheers!

       
      • 2 replies
    • Hi guys just to discuss with you my understanding of crack widths in Environmental structures according to ACI. 

       

      ---------------------------

      Normal structures

      ---------------------------

       

      1. ACI 318-95 based on statistical method of Gergely & Lutz 1968 limits Z based on exposure. We are calculating crack widths here. (Normal structures)

       

      2. ACI 318-99 proposed limiting the spacing and removed actually calculating the width and also removed the exposure conditions. For example for beams and one-way slabs s (in) = 540/fs -2.5cc or in other words limiting the fs=0.6fy  (For normal structures)

       

      3. ACI 224R-01 references method 1 and 2 above and 3 european codes.

      The most confusing part is the table in which Nawy suggests 0.1mm crack width for water-tight structures. The whole document is for normal structures except this line. And people are following this line and refer to this document for water tight structures. I mean its just a suggestion and by the way this method 1 is obsolete now since ACI 318-99 (see point 2 above).

       

      ---------------------------

      Water tight structures

      ---------------------------

       

      1. ACI 318-08 states clearly that for watertight structures ACI 350-06 codes should be used. 

       

      2. ACI 224.4R-13 also specifically states that for watertight structures walls in section 7.4, we should use ACI 350-06. 

       

      3. ACI 350-06 for water tight structures does not recommend calculating a number for crack width but rather limiting max steel stress in bars to be 20k ksi or fs=0.33fy for normal conditions.

       

      ---------------------------------------------------------------------------------------------------------

      To sum it up, 

       

      Philosophy of crack width control is not to calculate probable crack widths but to limit the max stress in steel bars.

       

      For normal structures: fs=0.6fy and for water tight structures fs=0.33fy
      • 1 reply
    • Hi

      I want to know the use of diaphragms in etabs. i discus many people who are use etabs but i can't get justified answer about the application of etabs.

      I read the Technical reference  of  Etabs, where they write about Diaphragms. i get two type of diaphragms (plate or shell and joint or beam). 

      My question.

      1. When do i use Shell diaphragms (if floor present ) 

      2.When do i use joint diaphragms ( grade beam level where no slab are provide) 

       

      NB: Diaphragms use to transfer the lateral load to the resisting element ( frame such as column. beam,shear wall) 
      • 2 replies
    • *SEFP Consistent Design*<br style="color:#272a34">*Pile Design*<br style="color:#272a34">*Doc No: 10-00-CD-0005*<br style="color:#272a34">*Date: Nov 21, 2017*<br style="color:#272a34">
       

      This article is intended to cover design of piles using Ultimate Limit State (ULS) method. The use of ULS method is fairly new for geotechnical design (last decade). The method is being used in multiple countries now (Canada, Australia etc). The following items shall be discussed:

      Overview


      Geotechnical Design of Piles (Compression Loads, Tension Loads and Lateral Loads)


      Structural Design of Piles (Covering both Concrete and Steel)


      Connection of Pile with the foundation (Covering both Concrete and Steel)


      Pile Group Settlement


      Things to consider



       

      1. Overview

      Piles provide a suitable load path to transfer super-structure loads to foundation where shallow foundation are not suitable - this can be due to a number of reasons like existing space constraints or suitable soil strata is not present immediately below structure. Other uses can be to meet design requirements like to have reduced settlement etc.

      This article shall cover the use of straight shaft cast-in-place concrete piles and straight shaft driven steel pipe piles. There are a number of additional piles types like belled concrete piles, precast concrete piles, screw / helical steel piles etc but the discussion to choose a suitable pile type is not in the intended scope of this article. The article is intended  to discuss design requirements for straight shaft piles only (both concrete and steel) . The aforementioned topic about pile selection is a very diverse subject and requires a separate discussion on its own.

      Click on the link to read the full article.
       
      • 9 replies
    • I am suppose to design a pile foundation for a machine weighing approximately 50 tons and with an operational loading of 100 tons. 
      I ll appreciate your help in terms of guidance & provision of notes...  
       
      Thank you..
      • 36 replies
    • Material behavior can be idealized as consisting of an 'elastic' domain and a 'plastic' domain. For almost 200 years, structural design has been
      based on an elastic theory which assumes that structures display a linear response throughout their loading history, ignoring the post-yielding
      stage of behavior. Current design practice for reinforced concrete structures is a curious blend of elastic analysis to compute forces and moments, plasticity theory to proportion cross-sections for the moment and axial, load, and empirical mumbo-jumbo to proportion members for shear.

       

      From the book "Design of Concrete Structures with Stress Fields" by A. Muttoni,  J. Schwartz and  B.Thurliman.

       
      • 0 replies
    • 9th International Civil Engineering Conference (ICEC 2017), December 22-23, 2017, Karachi, Pakistan
      Dear Fellow Researchers, Academicians, and research students,

       

      NED University of Engineering & Technology in collaboration with Institution of Engineers Pakistan (IEP) is organizing 9th International Civil Engineering Conference (ICEC 2017) on December 22-23, 2017 at Karachi, Pakistan.

       The congress details are available at its website www.neduet.edu.pk/icec

       Also attached is congress flyer for information and dissemination among your peers.

       Abstracts submission deadline has been extended till October 31, 2017.

      Please click on the link to see the full description.
      • 0 replies
    • AoA all,

      Is it mandatory to do column concreting upto the soffit of the beam in a single pour ?

      What code says about the construction/cold joint location in column ?

      Majority of the contractors are pouring the column concrete upto the soffit of the beam (full height of the column), some contractors leave the column height about 9" to 12" below the beam level and then fill this 9" to 12" column height with the beams & slab concreting. On one site column concreting was stopped at the mid height and the remaining half was filled on the next day.

      Thanks

       

       
      • 5 replies
    • AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       