can you please tell me,

Why foundation is designed for STATIC LOAD CASES only.

Why not we design foundation for RESPONSE SPECTRUM CASES.

In our office  for G+24 also we design foundation only  for STATIC LOAD CASES,  is it wrong if we do foundation for static load cases

Share this post

Link to post
Share on other sites

You should design it for seismic case too. With response spectrum analysis, signs are lost and maybe that's why your office is not designing foundations for it but technically speaking,  foundations need to be designed for all ULS Load Cases based on LRFD. 


Share this post

Link to post
Share on other sites

Earth quake loads consider in foundation designs as well in its sizing as well as in its structural design. If someone omits, it purely his own choice


Share this post

Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now

  • Our picks

    • Hi guys just to discuss with you my understanding of crack widths in Environmental structures according to ACI. 



      Normal structures



      1. ACI 318-95 based on statistical method of Gergely & Lutz 1968 limits Z based on exposure. We are calculating crack widths here. (Normal structures)


      2. ACI 318-99 proposed limiting the spacing and removed actually calculating the width and also removed the exposure conditions. For example for beams and one-way slabs s (in) = 540/fs -2.5cc or in other words limiting the fs=0.6fy  (For normal structures)


      3. ACI 224R-01 references method 1 and 2 above and 3 european codes.

      The most confusing part is the table in which Nawy suggests 0.1mm crack width for water-tight structures. The whole document is for normal structures except this line. And people are following this line and refer to this document for water tight structures. I mean its just a suggestion and by the way this method 1 is obsolete now since ACI 318-99 (see point 2 above).



      Water tight structures



      1. ACI 318-08 states clearly that for watertight structures ACI 350-06 codes should be used. 


      2. ACI 224.4R-13 also specifically states that for watertight structures walls in section 7.4, we should use ACI 350-06. 


      3. ACI 350-06 for water tight structures does not recommend calculating a number for crack width but rather limiting max steel stress in bars to be 20k ksi or fs=0.33fy for normal conditions.



      To sum it up, 


      Philosophy of crack width control is not to calculate probable crack widths but to limit the max stress in steel bars.


      For normal structures: fs=0.6fy and for water tight structures fs=0.33fy
      • 1 reply
    • Hi

      I want to know the use of diaphragms in etabs. i discus many people who are use etabs but i can't get justified answer about the application of etabs.

      I read the Technical reference  of  Etabs, where they write about Diaphragms. i get two type of diaphragms (plate or shell and joint or beam). 

      My question.

      1. When do i use Shell diaphragms (if floor present ) 

      2.When do i use joint diaphragms ( grade beam level where no slab are provide) 


      NB: Diaphragms use to transfer the lateral load to the resisting element ( frame such as column. beam,shear wall) 
      • 2 replies
    • *SEFP Consistent Design*<br style="color:#272a34">*Pile Design*<br style="color:#272a34">*Doc No: 10-00-CD-0005*<br style="color:#272a34">*Date: Nov 21, 2017*<br style="color:#272a34">

      This article is intended to cover design of piles using Ultimate Limit State (ULS) method. The use of ULS method is fairly new for geotechnical design (last decade). The method is being used in multiple countries now (Canada, Australia etc). The following items shall be discussed:


      Geotechnical Design of Piles (Compression Loads, Tension Loads and Lateral Loads)

      Structural Design of Piles (Covering both Concrete and Steel)

      Connection of Pile with the foundation (Covering both Concrete and Steel)

      Pile Group Settlement

      Things to consider


      1. Overview

      Piles provide a suitable load path to transfer super-structure loads to foundation where shallow foundation are not suitable - this can be due to a number of reasons like existing space constraints or suitable soil strata is not present immediately below structure. Other uses can be to meet design requirements like to have reduced settlement etc.

      This article shall cover the use of straight shaft cast-in-place concrete piles and straight shaft driven steel pipe piles. There are a number of additional piles types like belled concrete piles, precast concrete piles, screw / helical steel piles etc but the discussion to choose a suitable pile type is not in the intended scope of this article. The article is intended  to discuss design requirements for straight shaft piles only (both concrete and steel) . The aforementioned topic about pile selection is a very diverse subject and requires a separate discussion on its own.

      Click on the link to read the full article.
      • 9 replies
    • I am suppose to design a pile foundation for a machine weighing approximately 50 tons and with an operational loading of 100 tons. 
      I ll appreciate your help in terms of guidance & provision of notes...  
      Thank you..
      • 36 replies
    • Material behavior can be idealized as consisting of an 'elastic' domain and a 'plastic' domain. For almost 200 years, structural design has been
      based on an elastic theory which assumes that structures display a linear response throughout their loading history, ignoring the post-yielding
      stage of behavior. Current design practice for reinforced concrete structures is a curious blend of elastic analysis to compute forces and moments, plasticity theory to proportion cross-sections for the moment and axial, load, and empirical mumbo-jumbo to proportion members for shear.


      From the book "Design of Concrete Structures with Stress Fields" by A. Muttoni,  J. Schwartz and  B.Thurliman.

      • 0 replies
    • Dear Fellow Researchers, Academicians, and research students,


      NED University of Engineering & Technology in collaboration with Institution of Engineers Pakistan (IEP) is organizing 9th International Civil Engineering Conference (ICEC 2017) on December 22-23, 2017 at Karachi, Pakistan.

       The congress details are available at its website www.neduet.edu.pk/icec

       Also attached is congress flyer for information and dissemination among your peers.

       Abstracts submission deadline has been extended till October 31, 2017.

      Please click on the link to see the full description.
      • 0 replies
    • AoA all,

      Is it mandatory to do column concreting upto the soffit of the beam in a single pour ?

      What code says about the construction/cold joint location in column ?

      Majority of the contractors are pouring the column concrete upto the soffit of the beam (full height of the column), some contractors leave the column height about 9" to 12" below the beam level and then fill this 9" to 12" column height with the beams & slab concreting. On one site column concreting was stopped at the mid height and the remaining half was filled on the next day.



      • 5 replies
    • AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

      • 10 replies
    • Salam Members,

      Congratulations to Engineers, PEC has become full signatory of Washington Accord, what are the benefits to Pakistani engineers for this agreement. 




      • 3 replies
    • Please clarify the following confusions one by one:-


      1. If we run P-delta analysis in ETABS, then should we ignore stiffness property modifiers for beams and columns? I have heard that if we perform P-delta analysis and apply stiffness modifiers at the same time then the moment magnification process is doubled...?


      2. ETABS considers selenderness of a column by applying moment magnification factors. If we run P-delta analysis also, does it mean that the selenderness of column is being over-estimated? I mean once the moments are magnified in P-delta analysis process and again through moment magnification process?


      Please help me understand the software myth and clarify above confusions.
      • 1 reply
  • Recently Browsing   0 members

    No registered users viewing this page.

  • Similar Content

    • By Shamim Ahmmed
      Salam to all,
      Is there any rules to depth of foundation(Df)
      Say, I need MAT foundation on SBC=1.43 ksf.
      what would be the depth of Mat Foundation (Df) from Existing Ground Level.
    • By Muti Ur Rehman
      Assalamu Aalikum,
      Hi, I am a new member. I have a plot measuring 30*70 feet. Most of houses being built here (in Rawalpindi) have masonry foundations (a pyramid of bricks on PCC or sometimes the PCC layer has three to four iron rods of size 3/8 or 4/8  in this "PCC" layer. I want to make a raft foundation instead of masonry foundation but the cost seems to be high. I want to ask if I make a raft  1 feet thick and put a single mesh of center to center distance  12 inch. Even this will cost more but if it gives more strength then I want to  go for this. Would such foundation more durable and strong?
    • By Fatima Al Zahraa Olleik
      Dear fellow engineers,
      In a refugee camp reconstruction, we have the following dilemma:
      First, we have an existing retaining wall, height up to 4.5 meters, thickness ranging from 0.25 to 0.4 m. On the back of the wall we have existing an layer of cyclopean concrete :height up to 4.5, width 3m, and length along the wall.
      A 5 story building is to be built over the cyclopean concrete. This means that the Raft of the building (0.5m thick) will lie directly above the existing wall.
      The question is, what is the calculation required to ensure that this wall will withstand the loads of the raft?
    • By muneeb1213
      For calculating the bearing capacity of soil (using N values), the equations for mat foundation and single footings is the same or its separate for each??
    • By muneeb1213
      I m designing a 4 storey building on a poorly graded sand with SPN value of 5 and allowable bearing capacity of 0.5 tonn/sq.ft..... for the mat foundation, i provided beams of 18 x 36 and mat thickness as 24 inches ... however the soil pressure are still above safe bearing capacity.. My question is should i assign line spring property to the footing beams or not???
      The area of footing is also increased but the stresses are still high...
    • By Waqas Haider
      From engineering point of view, it is really very amazing to see a complete city builtup in water ways, in a lagoon. How did they make the foundation system of buildings completely all the time underwater? Really interesting article here is. It also explains some modern challanges to the city i.e. flooding due to raised levels of sea and an inteseting solution to this problem.

    • By Waqas Haider
      Assalam o alaikum, 
      i m confused whether collectors and chords are only required in Flat plates/slabs or also required in beam slabs? because in beam slab we are having beams at perimeter of every panel and they can act as chords and for diaphragm bending and as collectors at junction of slab to shear wall. Usually, in seismic zone 4, i dont design diaphragm exclusively. i just design it as simple slab and design my beams in SMRF or Dual Frame in etabs. 
      Also i m confused in excerpt from a document stating
      The Special Seismic Load combination is also indirectly identified in Chapter 18, Section 1809, Foundation Construction – Seismic Zones 3 and 4.
      1809.3 Superstructure-to-Foundation Connection. The connection of superstructure elements to
      the foundation shall be adequate to transmit to the foundation the forces for which the elements
      were required to be designed.
      For instance, since Section 2213.5 Column Requirements specifically identifies the Ω0 factor, Section
      1809.3 requires the column-to-foundation connection to be designed for a load combination which includes
      the Ω0 factor.
      What does it mean? In seismic zone 3 or 4, we need to design foundations for special seismic combos ALWAYS or only if we r having discontinuous system? The full document is also attached. Thanks.
    • By waqar saleem
      Dear Sefpians!!
      I have to design a foundation for a 15m high floodlight pole, dia of the pole is 10 inches, pole is welded with the baseplate (provided by manufacturer), how the forces will be transferred to anchors. what forces will be on anchors. how forces will be transferred from anchors to foundation. anchors will be embedded in-situ concrete.
    • By waqar saleem
      Dr.Amjad Saqib!!! I love this person for his efforts to reduce the poverty with dignity. Founder of Akhuwat Foundation speaks from his heart,wondefully . Listen to his speech at TEDx
    • By israr_sari
      How to  import multilevel raft foundation from etabs to safe.
      main designer has designed it as a raft foundation with a bearing capacity of 150 kn/m2 but after the site development and excavation we found a hard strata that can with stand with 250 kn/m2(as per the soil report). as total depth of raft is 1 m that is too much for 5 storey car parking, i want to modify it with 250 raft overall with inverted panels under column. but i am not able to import that multi level foundation reactions as a one file in Safe. because in etabs u can only export one storey . 
      please give your helpful suggestions.