Dear members
on this link there is a drawing in which top_reinforcement is just supported only on one side how this type of reinforcement is efficient.
http://wiki-edupunk.blogspot.com/2012/08/slabtopreinforcement.html
thanking you in anticipation for your precious time and knowledge sharing
actually the top reinforcement is provided on both the sides..bt there are two bars..
a standard bar length is usually 40 ft or 60ft or 12m etc
if the length required is greater than these standard lengths you have to make splices...there are many other reasons for which you have to split the bars and provide splices. Its normal...
Dear members
http://wiki-edupunk....nforcement.html
drawing is unclear as is your question. For me it seams like top reinforcement has been provided on all four sides at the spacing of half of bottom reinforcement.
Drawing shows top rebar on all sides
by both sides i mean in one direction...bt the top reinf is on all four sides.....
@waqar
this is normal! the moment at middle span is high because of 1 span (simply supported)...so if an alternate bar is provided at top...this is perfectly normal..yeah it will take stresses as far as you have provided enough reinforcement and with proper splice and development lengths...
thanx Rana sir as it is simply supported then it should not be cut before the support ,actually in drawing i am referring to the bar is cut before the support in case of fixed support we can provide necessary development length and cut the bar before support theoretically as we are providing top reinforcement for negative moment,here if it is simply supported why there is top reinforcement as there is no negative moment.
yeah you are right...if it is simply supported then theoretically! no moment at top and no required reinforcement at top!
but in reality we have some ethics :P for structures...and the CODE defines these ethics....so in reality we require bottom bars to be extended into supports....where practically there is no moment...(positve)
similarly the top bars are extended upto a length equal to developement length plus d after the inflection point
these minimum precautions are required to avoid failure in case of moment reversal and to provide structural integrity...
generally at the discontinous ends you need one third of positive reinforcement in case of simply supported slabs but due to curling of slab edges, torsion, and temperature shirnkage and due to relative stiffness of of the beams or supports there is a need to provide top reinforcement at discontinous ends...
thats y may be you have seen at some places that every other bar is bent up to give negative reinforcement area over masonry walls supports in our typical house construction in pakistan. means half of the positive moment reinforcement area is provided on discontinous egdes..
This is just a simply supported case of slabs resting on masonry walls...
In case of continous slabs resting on concrete beams the negative moment is some times more than positive...
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik