Service Load Combinations For Zone 3 For Footing Sizing
Waqas Haider
Assalam o alaikum,
Dear seniors,
I am to design a two story frame structure in Seismic zone 3. UBC tells me about two SPECIAL SEISMIC LOAD COMBINATIONS. For Zone 1, 2 A, 2B I use ASD load combinations for footing stability design i.e. bearing pressure check, uplift check, sliding check and over turning check. But for zone 3 should i include this special seismic load combinations for footing design also?? Section 1612.4 tells, for both ASD and LRFD the following special load combos should be used
1.2D + f1L + 1.0Em and 0.9D + 1.0 Em...................... for both ASD nd LRFD same combination?? I am very much confused and need urgent reply... Jazak Allah...
W salam,
UBC97 Section 1612.1 states "Buildings and other structures and all portions
thereof shall be designed to resist the load combinations specified
in Section 1612.2 or 1612.3 and, where required by Chapter 16,
Division IV, or Chapters 18 through 23, the special seismic load
combinations of Section 1612.4".
Hence it seems that these combinations don't intend for general design usage & should be only used where specifically required by code.
Further the requirement of special seismic load combinations is specified in code in only two provisions i.e "In design of elements supporting discontinuous members and collector elements, in sections 1633.8.2.1 and 1633.2.6 respectively" as follows,
  "1630.8.2.1 General. Where any portion of the lateral-loadresisting
system is discontinuous, such as for vertical irregularity
Type 4 in Table 16-L or plan irregularity Type 4 in Table 16-M,
concrete, masonry, steel and wood elements supporting such discontinuous
systems shall have the design strength to resist the
combination loads resulting from the special seismic load combinations
of Section 1612.4."
And,
"1633.2.6 Collector elements. Collector elements shall be provided
that are capable of transferring the seismic forces originating
in other portions of the structure to the element providing the
resistance to those forces.
Collector elements, splices and their connections to resisting
elements shall resist the forces determined in accordance with
Formula (33-1). In addition, collector elements, splices, and their
connections to resisting elements shall have the design strength to
resist the combined loads resulting from the special seismic load
of Section 1612.4."
Except these, no where in the code, these special load combinations are advised to be used.Therefore, allowable stress design combinations for your intended stresses evaluation should be independent of these special combos.
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik