Seismic Drift Procedure For Real Building
mhdhamood
Dear all;
I have prepared some procedures that in need to your evaluation according to your experience judgement.
I am saying that the following procedures that I will mention will be trusted after your comments that agree or disagree.
The procedure:
1. I get results from tables------> story drift as in pict.1.
2. Let us take one floor as a sample.For that floor we read the results of drift in x-direction as the maximum of
    all load combinations's results  that contain earthquake i.e six load combinations as shown in pic.2 .
3. Do the above for y-direction.
4. As a result the for 4th floor; Drift-x = 0.001986 and Drift-y = 0.001812.
5. Now what are the values we get and how to use it. These values coming from ETABS are representing the difference
    in elastic displacement between the floor and the floor beneath or up divided by the floor height
.(Please correct me if I am
   wrong).
6. Now to get the the seismic drift values from inelastic response we multiply the above drift by 0.7 *R .
    As an example let us say R=4.5 , then seismic drift-x =0.00625 and drift-y= 0.0057.
7. These values now are ready to compare with  ACI code limitations, Assuming fundamental period of structure=0.5  second:
     story seismic drift limit =2.5% * story height
8.  As you may see our story drifts either in x or in y are less than 2.5 %.
post-1776-0-42236900-1429599367_thumb.jp
post-1776-0-92450600-1429599369_thumb.jp
Mhdhamood,
The forum already has 2 complete detailed articles with examples that you can follow to confirm your understanding.
Here are the links:
http://www.sepakistan.com/topic/109-building-drifts-in-etabs/
http://www.sepakistan.com/topic/1341-ubc-seismic-drift-limits/
Dear Mr Umar;
I have read but here I see a difference in the two articles ;
Your article says that use for calculating seismic drift the ultimate load combinations from earthquake (three ones combine Dead+Live + spcx, spcy,spcxy and the other three that combines Dead+Spcx,Spcy,Spcxy)
But Mr Waseem says that using only single load cases SPCX  and SPCY....
which to follow ??
Strength design load combinations should be used to calculate the drift. Analysis should take into the account the reduction of stiffness of structural members, as well as, the effect the effect of gravity load acting on deformed shape ( second order analysis).
You can check the drift only against  against E. The difference is negligible for most of the structural configurations.
Dear Mr Umar;
which to follow ??
Mhdhamood,
For both cases, the factor with E is 1.0. It wouldn't make any difference.
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik