Blast Proof Retaining Wall
m_naeem_b
I did one and the reference I used was ,
Design of Blast-Resistant Buildings in Petrochemical Facilities
There is a solved example in it , calclations are simpe. You need to assume the load/ explosive weight and distance from load, calculate the shockwave velocity and proceed. I will check if I can find my calcs, but I am not sure I have it with me or not.
Regards,
  • 2 years later...
  • 9 months later...
  • 4 years later...
Dear Umar,
With reference to the example calculation in the design of blast resistant building. I have few queries.
1. What would be the case if Shear resistance is greater than bending resistance? its not explicitly defined in the guide.
2. If there is two way slab, what would be the case?
3. How are we comparing the strength of the section to applied load? does it has to with stand peak on side over pressure (Pso) or reflected pressure (Pr) for front wall. I am not clear about if section strength is compared to any loading .
4. If I model this scenario as Linear Time history analysis in STAAD and check support rotation limit of 2 degree. Is it correct.
Thanks alot.
Hi Rummaan17,
Great questions.
This can happen. However, just to keep things simple you can size your section to make sure bending resistance is > than shear resistance. I know this answer is not very neat but I have been out of touch with this so don't exactly remember the details here.
You might have to refresh me here about where does this come in play?
I think the example that I have provided only talks about the period calculation, not the strength. You are right. Do you have a criteria provided by the Client company to meet? There might be details there about what load combinations to use and what checks need to be done for blast loading for strength design.
Could be, but I haven't done it.
You have got some excellent questions here. I wish I could answer you better but to be honest, blast loading is a complete criteria in itself. Normally a good starting point would be client specifications that you have to meet as they should specify they load cases, acceptance limit states under strength and serviceability and any other items that need to be considered. If you don't have a governing criteria, then the next best thing would be to get a book on the subject and follow a design example and establish the limit sates. Let me know.