Response Spectrum Load Case
WR1
First of all my apologies, if my question seems stupid because of my unfamiliarity with the topic.
When defining response spectrum load case in ETABS, we have three directions; u1, u2 and u3.
Lets assume the excitation angle = 0 and building principle direction is u1
So I will apply response spectrum function (per IBC 2006) in u1 direction by a scale factor.
My question is why we don't apply u2 and u3 in the SAME LOAD CASE.
My understanding is, according to WILSON in his book on STATIC & DYNAMIC ANALYSIS, CHAPTER 15. The response is calculated for each direction separately. Then this response is combined by different methods (CQC, SRSS etc) which is called MODEL COMBINATION.
In CQC method response in 2 directions is assumed to be a portion of 1 direction means S2=a.S1
Where a = 0 to 1.0, recommended value is 0.50 to 0.85
I know in EQ building has only one principle direction. Although EQ can hit from any direction but there is always one major direction. or you can say major acceleration in 1 direction. Lets say u1.
As in CQC method the response in other direction will be some portion of response in major direction. I also know that If we have equal spectra CQC is reduced to SRSS method which is independent from the excitation angle theta.
My confusion is we will do MODAL COMBINATION (cqc or srss) only when we want to combine u1, u2 and u3 at the same time. But if we are applying only u1 in one response spectrum load case, then we DONT have to do modal combination. It is the same thing as in CQC S2=a. S1. Now in this case a=0. so S2=0. All we have is only response in u1 direction.
Then in my building models what i do? include u1 and u2 both in one load case or in separate load cases?
ok thanks...i understand what u said...my building is not regular thats y im concerned with orthogonal effect..anyways...i have this confusion:-
I understand that u cannot take both directions in one spectrum load case because it will be 100 and 100 which is not realistic..
but my point is why then CSI team has put this option in ETABS..they could have omitted u2 text box from there....there should be some reason why they put it?
  • 11 months later...
  • 4 years later...
On 11/21/2012 at 6:21 AM, UmarMakhzumi said:
You should define separate load cases.
It would help you understand mode shapes, assign scale factors so that modal mass to be 90% or whatever code criteria is, and make your combos compatible too.
Umar sb i am not clear bout this 90% contribution how do we check this and what is meant by this ? whatever the mode is there is contribution of mass either in direction X or Y.
Yar, it is a requirement that your model should include enough modes that the sum of mass participation of all the modes should be greater than 85 or 90 (whatever is in the code). You can download a tutorial that I posted some time ago that shows how to check this participation and how to scale the values. Check the link below.
  • 3 years later...
Aoa,  i was working on G+35 tower , I've preformed response spectrum analysis ,scaled dynamic base shear for more than 85% respect to static base shear, all the shear walls fails pu/po>.35 , initial sections sections were 12'' up to the top, i increased sections and fc'. but my senior told me not to increase size of walls instead replace  static Eq ( all six) load case with spectrum load case , he gave me reference of model which is done by other structural design firm. seniors here kindly elaborate what would be the reason not to include Static Eq cases in load combinations.
note. diaphragm is semi rigid
check attached excel sheets of load combos.other firm.xlsx
my model.xlsx other firm.xlsx
I am a bit confused by your question. My understanding is that you designed the structure for Response Spectrum loads and as well as for equivalent static loads and then your senior told you use response spectrum only and you want to know why is that ?
Depends on Building Code. For some structures with irregularities response spectrum analysis is mandated by codes since equivalent static is more applicable for regular shaped buildings with continuous load path and might not give  accurate seismic force distribution.
thank you for response . yes i agree, lda analysis should be preformed  for irregular structures, my confusion is about load combination, which load combinations should i use , RS only or both Static and Rs .
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik