Dr Yueh
Beam deflection  as shown in Etabs  is .757 in  . Is it uncracked section immediate deflection or cracked section immediate deflection??  Note All property modifiers are 1 (as default) .
Dear Saiful Islam,
Immediate deflection vs long-term deflection is one issue.
Linear analysis vs non-linear analysis is another.
In ETABS, generally we are almost always performing linear analysis. That means deflection is directly related to the load applied without long-term non-linear effects. So let's ignore non-linear analysis for a moment.
In linear analysis, now the question is how do we get immediate and long-term deflection.
Immediate deflection could be non-cracked deflection or cracked deflection. Practically speaking, long-term deflection will always be on cracked sections. Although anything "cracked" is essential a non-linear problem, but here let's stick to out point of doing linear analysis only.
Now, generally we are not interested in immediate non-cracked deflection. This leaves us with cracked - short-term & long-term deflections in LINEAR analysis.
As you are doing LINEAR analysis in ETABS, you cannot get cracked deflections directly. For this, you may apply stiffness reduction modifier option available in ETABS.
As you are not applying any stiffness reduction modifier, that means, its NON-CRACKED. This is the answer to your question. However, exploring further, if you want to obtain long-term deflection, you can multiply the immediate deflection by a long-term factor given in ACI chapter 9.
Now comes the non-linear analysis: You can use SAFE for non-linear analysis and get long-term cracked deflections (non-linear) without using modifiers. The cracked non-linear analysis in SAFE will give you long-term cracked deflection which will depend on the extent of cracking which will depend on the reinforcement which will depend on the moment applied. This moment again will depend on the stiffness of cracked section including the reinforcement. So you see, its a non-linear iteration problem.
To read further about, linear vs non-linear and elastic vs inelastic analysis, please refer to the book 'Modelling for structural analysis' by Powell.
2 hours ago, Saiful Islam Zaber said:
I Know how to calculate long term slab deflection using SAFE .. How to find BEAM long term deflection using SAFE??
Same procedure.
On 7/10/2017 at 0:04 AM, Rana said:
Same procedure.
I will be grateful to you if you tell me how to check beam deflection. when i click " Show deformed shape" SAFE represents only slab deformation for certain combination
  • 9 months later...
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik