Girts and Purlins affect of Column Beam Effective Length
Salma Jabeen
Yes purlins and girts provide lateral restraint to rafter and column, respectively..
Rafter
·         For calculating minor axis compression capacity, the effective length of the rafter is taken as the maximum spacing between the                    purlins.
·         When the rafter’s top flange is in compression the effective length of the rafter is taken as 0.85 x purlin spacing for calculating out of             plane capacity.
Column
·         For calculating minor axis compression capacity, the effective length of the column is taken as the spacing between the girts.
·         When the column’s outside flange is in compression the effective length of the column is taken as 0.85 x girt spacing for calculating                out of plane capacity.
Can we increase this 0.85 to 1.0 (as it appears logically).
Really helpful if relevant  literature is referred for the sake of interest and further reading.
Edited by MA123
Rafter
Column
@Ahmed1, where you say minor axis compression capacity, do you mean minor axis flexural capacity for compression flange?
@ MA123
This factor will depend on end condition of the member.  Increasing to 1 will reduce axial compression capacity for buckling.
@ Ayesha
I was referring to axial compression capacity for buckling (Ncy) required for checking the member for combined actions.
On 8/24/2018 at 7:01 PM, Ahmed1 said:
@ MA123
@ Ayesha
I am  not sure what the reference is but this formula should be for a member being used as column, not as beam. Beam would never have significant axial load (generally speaking) so why use this formula?
  • 4 weeks later...
  • 9 months later...
Hello everyone. Extending on Salma's questions, will the purlins be sufficient as bracing elements against lateral torsional buckling of straight simply supported beams?
LTB has to do with compression flange being braced against side sway movements so yes, the purlins can be effective in my opinion. I haven't done a lot of design that used purlins so might be better if @Ahmed1 can reply as it looks that he has some experience in this field.