Calculating Partition Wall Load on Slab
Muhammad Munaf
Can you explain more. Are you having problems "calculating" the load or "applying it"
Here is the traditional way to calculate the load. Calculate the volume of the partition wall and multiply by density of material. That will give you the total load of the partition wall. Divide it by the length of wall and you have a linear load that you can apply using dummy beam.
Wall Load per running foot = (Wall ht.)(Wall Thickness)(Unit wt.)
Suppose you have 9inch thick wall of ht. 12ft and unit wt. of clay masonry brick is 120lb/cft.
Wall Load/Rft =(12)(0.75)((120)=1080 lb/ft =1.08kip/ft
Line load would not be assigned directly to area element (slab,wall). So assign a dummy beam and apply line load to this dummy beam.
Wall volume = Hieght x length x Thickness ( all units are in feet)
Wall Load ( point load ) = Wall volume x 120 lb/cft
Wall load on slab = wall point load / area of slab ( Gives load in lb/sft i.e psf)
in software assign it as Super dead load
On 5/13/2019 at 4:10 AM, Tufail Mabood said:
Why Super Dead Load? Can you elaborate Please?
It helps with the checking. When you assign it, you can easily compare between structural dead weight and the weight of partitions.
  • 9 months later...
With "Initial structural design" and sizing I use these loads - these can be checked / verified further, if needed, at detail design. These figures always work. Loading should be generous at "initial design stage".
These are the blanket UDL "dead loads" figures that I use, say for an office building design:
Floor finish - screed/tiles : 1.8 kN/m2 ( 35psf);
Ceiling and Services 0.5kN/m2 (10 psf);
Lightweight partition system : 1.0kN/m2 (20 psf)
Concrete block/brick partitions - 2.0kN/m2 (50 psf) - you can also check these as line loads at detail design is floor to ceiling heights are high, or  lots of close blcok partitions exist.
Over the design life of a building, say 50 years, the partition and finishes can change - design safe.
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik