Torsion Longitudinal Reinforcement
Rifat
Dear,
As salamu alikum.
I have a query. I designed a beam (12"x 24") which required bottom longitudinal rebar area is 2.00 in2  & top longitudinal rebar area is 1.50 in2. Required combined with flexural and axial reinforcement (torsion) area is 1.2 in2.
My question is how to provide the torsional rebar in this beam how its arrangements.Though my bottom longitudinal rebar area is more than torsional reinforcement then is  it necessary to provide more 1.2 in rebar? What is rules?
Thanks in advanced
ASK
According to ACI, Torsion longitudinal reinforcement should be equally distributed to the 4 faces of the beam
and
ACI 318 says that the torsion reinforcement is additive to the required flexural reinforcement
in your case, u can distribute the steel in  2 top corner bars + 1 side bar + 2 bottom corner bars
( Addl to top & bottom Flexural reinforcement )
regards
The information provided by Mjnasar is correct:
On 10/16/2019 at 2:35 AM, Rifat said:
Dear,
As salamu alikum.
Thanks in advanced
Also, take care that the torsional shear reinforcement = area of only outermost 1 closed stirrup. In other words, make sure the outermost continuous big stirrup (have 4 legs all around) is sufficient to carry all torsional shear. You can't distribute in among internal stirrups.
However, you can provide multiple stirrups (verticals legs only effective) for flexural shear.
Also, if one stirrup (flexural or torsion) is not enough, provide 2 bundled stirrups side by side along beam length or reduce spacing.