Cut off point of extra bottom bar of continuous beam at support
Rifat
Hello,
As salamu  alikum.
I want to verify if my judgement (as shown in figure below) is correct. .
We know that the extra top bars of a continuous beam would terminate at the middle third from the support . and the extra bottom bars at mid span would terminate usually at quarter length of the beam.. but what about the extra bottom bars at the support ? is the figure above correct? is there any section of the aci code that would verify this.. will the cut off point be the same for tie beams, grade beam , 2nd story and above beam?
Thanks in advance
Based on European - Eurocode detailing rules (they are often more onerous - always safer than ACI code).
1. Bottom bars at support in beams and slabs should be bent into wall / columns support always. The key flexural bars are the top ones, and they should always bend into wall / column support to cater for the -ve hogging moment at supports!
2. If there is enough depth of slab, I prefer to use U-bars ...great for Pakistan where there are seismic factors etc. U-bars are ideal but not possible in all cases due to congestion of reinforcement.
3. For a safer approach, 50% of BOTTOM reinforcement should be taken through the external supports.  All the top reinforcement to suit hogging moment.
For Internal supports the requirement is for BOTTOM reinforcement is for 30% minimum of the reinforcement  taken through the support.
Therefore work to 50% in all cases for BOTTOM reinforcement for safer option.
Curtailment of reinforcement rules to reflect bending moment, and lap length and minimum anchorage rules all apply when detailing.
I prefer the some beam bars to be taken within 50mm of support face - just stop short - see second figure below.
Hope this is helpful. Why don't we have a Pakistan Reinforcement Detailing Manual?
With ACI codes bottom bar must go into the support a min of 150mm; I know there are variations to this - For robustness of structure bottom bar MUST always go into the column/wall support. I always prefer to provide full anchorage of bottom reinforcing bar into support.
In seismic regions there is always forces variations whereby +ve moments can become -ve under cyclic loading, and vice-versa - hence best to have a robust detail.... U-bar ideal other provide full anchorage of bottom bar into the support, ideal for cyclic loads.
Therefore, ALWAYS detail bottom bar into support - beam into column same detail as previously suggested.
If I read it correctly, you are interested at the bottom bar at the support as shown in the figure.
The requirement of that bar depends on the kind of loads you will expect and load direction. For example, in gravity loads, for a moment frame, the requirement of reinforcement is at midspan for bottom bars and at support for top bars. So, for the reason, you curtail re-bar at bottom from entering support (non-seismic, gravity) is the same reason you would need minimum re-bar at the support.
If you have a grade beam, the direction of loading changes, and so does +ve moment faces and re-bar detailing.
Hello,
As salamu  alikum.
Thanks in advance
This case would usually occur if there is a two span beam with one span having high bending moment and the other one with lesser bending moment demands. In such cases all you need to care about is the development length so that full yield capacity of the bar in high bending moment section is achieved and further you can curtail the bar anywhere near the support. For grade beam the case is opposite i-e top bars will have to be curtailed at same specific location.
Edited by abbaskhan2294
First of all I'm having difficulty in understanding what does the OP mean by extra bars?
IMO the actual curtailment of rebars should be based on the moment envelope and the required development lengths.
What do you mean by OP?
What do you mean by IMO?