Rcc dual system design in ETABS
Hassaan
I need help on the below mentioned query;
My query is dual system design in etabs for 24 story Rcc building.
Once the parent etabs model is finalized after all the stabilty checks then we have to find base percentages for both columns and shear walls.
And prepare two separate models
One for columns and beams design  and the other for shear wall design.
For these two models where and what we have to modify.
If anyone have the reference document  for the detailed procedure of dual system design or any reference etabs model
Will be grateful for your response
In a dual system, you'll design your shear walls to cater for lateral loads and moment resisting frame will take care of gravity loads. Mostly in dual systems, it is considered a good practice to make your moment resisting frame system strong enough to withstand at least 25% of total base shear.
So here's what you can do; when designing walls against lateral loads, (EQ and Wind), assign moment releases to beams. This will mean that all lateral forces are being taken up by shear walls only.
As for your Moment resisting frame design, delete shear walls and in your Static Earthquake load cases (ELF), assign 0.25 scale factor instead of 1. This will ensure that your moment resisting frames are being designed to account for 25% base shear as well, along with gravity loadings. (You can call this emergency backup)
Perform above procedure and you are good to go :)
I hope this helps.
Edited by Howard Roark
Thanks foe your time and sharing valuable information.
One more thing,
Do we have to modify the scale factor of mass source to 0.25 as well..?
Furthermore, do we have to check and verify  our drifts from parent model, where no modification is done?
  • 2 months later...
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik