Piled raft
Muhammad Hashmi
Assalam O Alykum
I want opinion from seniors on the following
1. I am working on raft pile cap and piles will be designed by company name swiss boring most probably.
If I reduced the stiffness of of raft pile cap to 0.25 and compare that reaction value with the pile capacity is it good approach what do you suggest. Its over conservative I know, but the problem is that geotechnical specialist who gave the values of pile capacity etc. not having good reputation.
2. Any code that recommends the safe boring distance between piles.
Apologise small addition, I also ignore the subgrade reaction under the pile raft and consider 7500 Kilonewton per meter cube. However, in geo tech report it's mentioned 20,000.
Thank you
Edited by UmarMakhzumi
Merged Two Posts.
7 hours ago, Muhammad Hashmi said:
"Any code that recommends the safe boring distance between piles"
Hashmi,
For steel piles that are hammered/ driven in the ground: 2.5 * Outer Diameter of the pile is the minimum distance that is kept in Canada (I think this comes from Canadian Foundation Engineering Manual but can't recall the reference). This is out general accepted practice but normally we want to keep the minimum distance as 3.0* Outer dia of pile. If that can't be achieved then we go for 2.5*D but never lower than that. Sometimes, the piles will heave a little out of ground when adjacent piles are being driven (even with keeping 2.5-3 *D) distance. Such piles should be re-tapped.
Thank you.